    Wiring 4 wire outlet w/only 3 wires
    My wall outlet is a 3 prong and I want to convert it to a 4 prong but I only have three wires?
    Should I make a jumper in the outlet from the common to the 4th grounding outlet?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 19, 2008, 01:24 PM
    Would you please let us know exactly why you want a four prong outlet.

    What are you going to connect to this outlet? What voltage and amperage will the load need? What is installed there now, voltage and amperage?
    maddmann225's Avatar
    maddmann225 Posts: 2, Reputation: 1
    New Member
     
    #3

    Aug 19, 2008, 02:08 PM
    Quote Originally Posted by donf
    Would you please let us know exactly why you want a four prong outlet.

    What are you going to connect to this outlet? What voltage and amperage will the load need? What is installed there now, voltage and amperage?
    Sorry, I have a 4 prong 220/240v dryer. The house is 30+ yrs old and has a 4 prong outlet that a previous owner installed in place of the original 3 prong. But the 4th ground post was left un-wired.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #4

    Aug 19, 2008, 02:34 PM
    That is a potentially dangerous situation, did you have an inspection done before you bought the home? Not that they would catch that anyway.

    Your choices are limited here, either replace the receptacle with a 3 prong or run a new cable and keep the receptacle. Connecting the neutral to the ground prong on the receptacle is not something you should do.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Aug 19, 2008, 02:48 PM
    Okay, do you have the installation instructions for the electrical requirement for the dryer?

    If you do verify whether you need a four wire connection point. If you do, then you must follow the instructions.

    That would mean you need to pull a new four wire cable to the receptacle outlet and properly install the receptacle. Most electrical dryers are 120/240 units using 30 amp, which means you would want # 10/4 AWG copper cable.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Aug 19, 2008, 02:52 PM
    The dryer almost doesn't matter. If all you have is a three wire circuit run then you can ONLY do as Tev suggests. Re-install a 3-wire receptacle, or run a new circuit and install a 4-wire receptacle.

    The receptacles dictates the dryer cord, NOT the other way around.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Aug 19, 2008, 02:57 PM
    The dryer's instructions dictate the necessary wiring.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #8

    Aug 19, 2008, 03:21 PM
    Too add, New construction require 4 wires for Dryers and Ranges, it's a good thing, keeps ground from carrying current.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Aug 19, 2008, 03:44 PM
    Quote Originally Posted by Stratmando
    Too add, New construction require 4 wires for Dryers and Ranges, its a good thing, keeps ground from carrying current.
    Just to make things clear, older 120/240v dryer circuits were allowed to have two hots and a neutral. A ground was not required. The neutral served as both the neutral and ground. A neutral was always required.
    This was allowed under certain specific instances.

    Newer codes disallowed the old "3-wire" dryer and range circuit making a dedicated grounding conductor necessary.

    If an old 3-wire dryer circuit exists there is nothing saying that you have to change it. It would definitely be a good thing to upgrade to a current "4-wire" circuit, but it is not mandatory.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #10

    Aug 19, 2008, 05:41 PM
    I agree, for this, 3 wire sounds best.
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #11

    Aug 19, 2008, 08:48 PM
    donf is right also, he should check his dryer instructions. I do believe that most dryers you see can be wired with either plug depending on an internal jumper. The poster should be aware of whether HIS dryer can be prior to making a discission on which route to take.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #12

    Aug 20, 2008, 04:26 AM
    That's pretty much the reason I said the dryer "almost" doesn't matter.
    Every American residential dryer I have ever seen has been 120/240v and convertible as far as the cord goes.

    240v European style models are a different story.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

230 volt welder with 2 wires outlet with 3 wires. [ 7 Answers ]

Hello. I have an older stick welder that has a ground, white wire and black wire. The outlet I have to connect to has a ground, black, white and red wire. Is there a way I can connect the old welder to the newer wires? I know the red and black are hot but what about the common white wire? What...

3 white wires twisted together from outlet box [ 1 Answers ]

I am trying to install a new light fixture where I had a ceiling fan. The problem I have is that the light fixture I am using has a "fast attach receptacle". The box where the old fixture was has a bare ground wire, a black wire, and 3 white wires twisted together. The white wires twisted together...

GFI-6 wires to one outlet [ 1 Answers ]

My question is that I have an outlet in the bathroom right next to the sink. (Big NO NO) This outlet has 3 whites to it and 3 blacks to it with the proper grounds. This would place it in the middle of a series. How do I distinguish the line and the loads to replace the outlet with a GFI Outlet??...

Mixing wiring and outlet wire gauge . [ 5 Answers ]

If I have a 15 amp circuit, and 14 gauge wire, why can't I install a 20-amp outlet? If a 20-amp device is plugged into the outlet, won't the circuit trip, preventing overload? Also, 20-amp outlets and 15-amp outlets appear to have the same connection for devices (two prongs and a ground hole),...

240 volt four wire in 240 three wire outlet [ 1 Answers ]

I have a generator that has (2) 20 amp 110 outlets and (1) 240 outlet. The 240 outlet have receptacle for four wire plug but I want to use it in a three 930 wire 240 volt plug at other end. Is this a workable solution?


View more questions Search