    Effluent pump or Grinder pump??
    Hi all... First, here's the background info:

    We’re in the process of finishing our basement. Due to the lot being a walkout and the builder wanting to get down to bedrock the basement has 12' ceilings. Because of that, he chose to have the main sewer line exit the house about 4-5' up the foundation wall as opposed to through the floor / under the house because there would have only been about .25" of drop to the city sewer line.

    Due to this setup he pre-installed a pump basin in the basement floor directly below the sewer line exiting the house. It’ll take appx. 6-8' of pipe to get from the pump up to the main sewer line. There’s already a 'Y' adapter in to connect the drain from the basin to the main line, and a vent line is installed ready to be connected. He plumbed the floor drain in the furnace room to drain to the basin, and stubbed out for a bathroom (shower, stool, and sink) and plumbed it to drain to the basin as well.

    We’re adding a kitchenette too and a sink for my shop. The basin will therefore service 3 sinks (1 having a disposal), 1 dishwasher, 1 shower, and 1 stool.

    Now the question:

    There’s a significant $ diff for an effluent pump vs. a grinder pump. We're trying to decide which way to go. Our research has shown effluent pumps handle up to a 2" solid, whereas a grinder doesn't really have a limitation since it grinds everything into slurry. The only possible >2" solid that could get to the basin would be from the stool. With a disposal on the kitchenette sink, not to mention a 1.25" drain line, nothing 2" is going to come from it or any other fixture. The rest of the house is not and will not be serviced by whichever pump we install.

    Can we get some feedback from the plumbing pro's here as to whether we should go with an effluent pump or a grinder pump? What the typical setup is and what the recommendation would be for their customers? What would you do if it were your home?

    Thanks very much in advance!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Feb 23, 2010, 04:54 PM
    My opinion, hands down, go with the effluent pump. I recommed the ZOELLER unit at www.zoeller.com . Simply put, these pumps are super reliable, reasonably priced and require very little maintenance.

    In 30 years I've been able to compare the sewage ejector with the grinder pumps and although the grinder pumps are nice they seem to have a tendency to break down after awhile, get noisy and are very hard to repair. They are EXTREMELY expensive to replace!

    The biggest issue with the ejector systems seem to be odors. This can be eliminated by running a dedicated vent (as you mentioned you have) and installing the seals provided properly. I follow up by placing a bead of flexible silicone sealant at all surfaces that mate up to the pipes and the lid edges. Otherwise, I have never had any complaints with these pumps unless someone tossed a tampon down the toilet and into the pit and that would mess any pump up!

    With any pump/grinder be aware you cannot let tampons, paper towels, tooth floss, or mop strings or simlilar enter the pit. These will get tied up around the impeller and cause the pump/grinder to fail or burn out.

    Anyway, I see no compariosn here! Go with the effluent pump!

    Mark
    cornman's Avatar
    cornman Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 24, 2010, 05:57 AM
    Thanks Mark!

    I guess I really meant Ejector pump as opposed to Effluent pump, my bad! I realized that they are in fact different after doing a bit more searching around.

    Let me ask an additional question...

    Some of what I've read indicates it is better to go with a NON-Automatic pump and add a supplementary float switch to automatically activate it. This way, if the switch goes bad you can replace it very easily as opposed to if it is an Automatic pump with a built in float switch. In terms of pricing, it looks like the cost of a NON-Automatic pump is less, but only by about the cost of an add on switch, so in the end the price is probably pretty much the same between the NON-Automatic and Automatic pumps.

    Thoughts?


    Quote Originally Posted by massplumber2008 View Post
    My opinion, hands down, go with the effluent pump. I recommed the ZOELLER unit at www.zoeller.com . Simply put, these pumps are super reliable, reasonably priced and require very little maintenance.

    In 30 years I've been able to compare the sewage ejector with the grinder pumps and although the grinder pumps are nice they seem to have a tendency to break down after awhile, get noisy and are very hard to repair. They are EXTREMELY expensive to replace!

    The biggest issue with the ejector systems seem to be odors. This can be eliminated by running a dedicated vent (as you mentioned you have) and installing the seals provided properly. I follow up by placing a bead of flexible silicone sealant at all surfaces that mate up to the pipes and the lid edges. Otherwise, I have never had any complaints with these pumps unless someone tossed a tampon down the toilet and into the pit and that would mess any pump up!

    With any pump/grinder be aware you cannot let tampons, paper towels, tooth floss, or mop strings or simlilar enter the pit. These will get tied up around the impeller and cause the pump/grinder to fail or burn out.

    Anyway, I see no compariosn here! Go with the effluent pump!

    Mark
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Feb 25, 2010, 01:37 PM
    Purchase an ejector with the integral float. Float switches are notorious for failing and having to be replaced periodically. They also have a tendency to get hung up on things that would never hang up a float on an ejector with the float attached.

    Mark

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Effluent pump pit vent [ 2 Answers ]

I have an effluent pump in my lower level. When I had the house built several yrs. Ago I hired a plumbing company to do all the plumbing. My effluent pump had to be replaced after seven yrs. And it was at this time that I found out there was a vent hole in the pit cover which was capped off with...

Why would the pump/grinder make noises when there is nothing in the catchbasin? [ 3 Answers ]

I have been awakened several times in the early morning hours recently by activity in the pumps. The grinder and/or the ejection pump (two separate power cords supply power to each device) operate at times when I wouldn't expect them to run. The basement bath & toilet don't get as much use as the...

Grinder Pump [ 7 Answers ]

Hello, My home is 10 years old and my sewer grinder pump located in the basement won't turn off. The only thing to drain into the basket for 9 years was the AC condensate and the water softner discharge. This year I finally hooked up a sink and toilet in the basement. All has been fine until...

Sewage/Grinder Pump not coming on. [ 2 Answers ]

For the past two weeks, my basement sewage pump has not been coming on all the time when needed. I called a plumber the first time, for water was starting to seep out of the top. I didn't hear the pump kick on during my morning routine, so I ran the tap and watched and waited and then water...

Inline vent fan with grinder pump [ 1 Answers ]

Has anyone every installed an in line vent fan to vent air to the outside for their plumbing system,especially if using a grinder pump...


View more questions Search