    Is this panel overloaded?
    I recently purchased a seasonal home 600sqft (lower NY state). The only source of power is electric. I did major renovations and expanded the curcuits in the panel. I need to understand what I have and if I need to upgrade service to the house or replace the panel.

    1- The main panel has what looks like 2 100amp lines entering it (240v). Is this considered 200 amp service?

    2- I expanded the panel to include a bunch of new circuits. I had to buy a few (3) double breakers 120v (2 switches in the same space that one had taken). Is this a problem? Should I be concerned about this? How can I tell if my panel has too many circuits in it?

    I’ve added a bunch of fixtures-
    7 recessed lights
    2 ceiling light fixtures
    1 bathroom fan + light
    Floor heat in the bathroom
    Dishwasher
    Micro hood combo
    2 - 8' strip lights in the garage
    Alarm system


    I’ve detailed below what the panel configuration is now-
    I had the following in the box before I touched it-
    240v - 30amp water heater
    240v - 50amp stove & cook top
    240v - 20amp well pump
    240v - 20 amp heater #1
    240v - 20 amp heater #2
    240v - 20 amp heater #3
    120v - 15 amp kitchen
    120v - 15 amp bathroom
    120v - 15 amp lighting & wall outlets
    120v - 15 amp lighting & wall outlets

    I added-
    3 more circuits for the kitchen
    15amp dishwasher
    20amp micro hood
    15amp lighting (reused 120v - 15 amp kitchen)
    20 amp circuit for countertop outlets
    Reused 240/50amp stove circuit

    2 circuits in the bathroom
    Reused 120v - 15 amp bathroom for lighting
    Added 1 20amp 120v circuit for heat

    Added
    15amp lighting circuit for the bedrooms

    Added-
    50amp 240v breaker feed for garage sub panel (6/3 direct burial ~65ft total length)
    The garage panel has one 15amp lighting circuit and 1 20amp circuit for a wall outlet. (I separated the neutral and ground on separate bars in the subpanel)
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Feb 15, 2010, 07:01 PM
    You say the main panel has 2 100amp lines coming into it? There must be a main breaker somewhere for this panel, what is the breaker size... 100 amp? Considering the size of this panel, I'll bet it's a 100 amp service, and if it is, you have certainly brought it up to it's capacity, and to the point of overload. Consider changing out the service.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do you remove the front toe panel on a Kenmore Elite Dryer? Is is only a panel. [ 1 Answers ]

I need to get under the dryer to replace a heating coil I guess. Dryer Not Drying but I cannot get the toe panel off.

Is my 100 amp panel overloaded? [ 5 Answers ]

My main panel is 100 amps and was completely full with about 10 breakers. About 5 years ago I had an addition put on the house and the contractor said that the service would need to be upgraded (but didn't specify how). After the licensed electrician left ,I realized that he had installed a...

Did one leg of our 1950's 100 amp main breaker fry because it was overloaded? [ 1 Answers ]

Did one leg of our 1950's 100 amp main breaker fry because it was overloaded by too many dedicated circuits? We have a main breaker with two "legs" outside our house and our main panel inside. Last week, an electrician installed 4 new dedicated circuits -- one each for microwave, kitchen...


View more questions Search