    Sub panel
    Here's my question. I removed an electric range top and replaced it with a gas one. I now have a 220 line left over. I would like to use it for a sub panel. I need a 120. Line for the gas range top,I also put in a microwave over the range. I would also like to put in a line for some cabinet accent lights. Could I use thesubpanel to run two 15 amp breakers and a20 amp breaker for the microwave? The 220 line is only 10gauge 30 amp cable. Or do I have to run new homeruns.
    Thanks Jim
    cdad's Avatar
    cdad Posts: 12,700, Reputation: 1438
    Internet Research Expert
     
    #2

    Feb 11, 2010, 07:04 PM

    What is the 220 line rated for? What size breaker is on it? That's what will give you your 110 rating. Its always best to run a new line but if your going to sub it out and split it then the amps are doubled to 110.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Feb 12, 2010, 03:36 AM
    Yes you can use the #10-3 with ground cable connected to the 30 amp breaker for a two or four circuit subpanel.
    luckyrabbit7's Avatar
    luckyrabbit7 Posts: 52, Reputation: 1
    Junior Member
     
    #4

    Feb 12, 2010, 11:23 AM

    Thanks for the replies. I had another question about the sub panel.
    Are the grounds and neutrals supposed to be on separate bus bars and the panel should not be bonded to the ground bar.
    luckyrabbit7's Avatar
    luckyrabbit7 Posts: 52, Reputation: 1
    Junior Member
     
    #5

    Feb 12, 2010, 11:24 AM

    Thanks for the replies. I had another question about the sub panel.
    Are the grounds and neutrals supposed to be on separate bus bars and the panel should not be bonded to the ground bar.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do you remove the front toe panel on a Kenmore Elite Dryer? Is is only a panel. [ 1 Answers ]

I need to get under the dryer to replace a heating coil I guess. Dryer Not Drying but I cannot get the toe panel off.

Wiring from my house panel to my pole barn panel [ 1 Answers ]

I am going to be wiring my pole barn up soon and just need some help on the type of wire to use. In my house I have a 200 AMP service and plan on running a 100 AMP feeder from that panel to my subpanel in the barn. (Just under 100 Feet) I am going to run a 6 gauge ground, two 4 gauge...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...


View more questions Search