    Sub panel
    Here's my question. I removed an electric range top and replaced it with a gas one. I now have a 220 line left over. I would like to use it for a sub panel. I need a 120. Line for the gas range top,I also put in a microwave over the range. I would also like to put in a line for some cabinet accent lights. Could I use thesubpanel to run two 15 amp breakers and a20 amp breaker for the microwave? The 220 line is only 10gauge 30 amp cable. Or do I have to run new homeruns.
    Thanks Jim
  • Feb 11, 2010, 07:04 PM
    cdad

    What is the 220 line rated for? What size breaker is on it? That's what will give you your 110 rating. Its always best to run a new line but if your going to sub it out and split it then the amps are doubled to 110.
  • Feb 12, 2010, 03:36 AM
    tkrussell
    Yes you can use the #10-3 with ground cable connected to the 30 amp breaker for a two or four circuit subpanel.
  • Feb 12, 2010, 11:23 AM
    luckyrabbit7

    Thanks for the replies. I had another question about the sub panel.
    Are the grounds and neutrals supposed to be on separate bus bars and the panel should not be bonded to the ground bar.
  • Feb 12, 2010, 11:24 AM
    luckyrabbit7

    Thanks for the replies. I had another question about the sub panel.
    Are the grounds and neutrals supposed to be on separate bus bars and the panel should not be bonded to the ground bar.