    What size should the neutral be if I run a 200A service using #1 copper?
    I am running 2, 100 amp disconnects off a 200 amp disconnect. The run is 100 feet long. I am told that I can use #1 copper for the power lines. What size should the neutral and ground wires be for this run?
    InfoJunkie4Life's Avatar
    InfoJunkie4Life Posts: 1,409, Reputation: 81
    Ultra Member
     
    #2

    Feb 10, 2010, 12:12 PM
    I believe the neutral is required to remain the same size, however the grounding wire may actually be allowed to be smaller. I'm not sure of the exact amount, but I believe it can be found in NEC #250-66.

    I don't have a NEC book available, and I couldn't find the table online...

    Good Luck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Feb 10, 2010, 02:05 PM
    The NEC is available on line as read only:

    NFPA 70: National Electrical CodeŽ

    Table 250.66 is for the grounding electrode conductor, which is the "ground" wire connected to the water main and/or ground rod(s), not the "neutral", AKA grounded conductor of a feeder.

    The neutral of a feeder can only be reduced 70% of the ungrounded (live)conductors IF the unbalanced current is calculated.Not worth the trouble, use a #1 for both live and neutral conductors.

    The "ground" of the feeder to the panel(s) is called the equipment grounding conductor, and is sized according to Table 250.122, that refers to the ampacity of the overcurrent protection device, AKA circuit breaker.

    For a 100 amp feeder, a #8 copper with green insulation, is the minimum size allowed.
    InfoJunkie4Life's Avatar
    InfoJunkie4Life Posts: 1,409, Reputation: 81
    Ultra Member
     
    #4

    Feb 10, 2010, 02:36 PM

    I know the difference between "Grounded" and "Grounding" and I was sure the grounding line could be reduced in size, but the only reference I found online to how much 250-66. Thanks for the clarity... I've seldom followed codes, it just seemed illogical to me to use a reduced neutral. Generally I use the same gauge wire for Neutral, Live, and Ground.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Feb 10, 2010, 05:07 PM
    Info, perhaps you do know, but the poster certainly does not, and that was what I was trying to address.

    Attempting to illustrate that the term "ground" is widely misunderstood, or misused, and the only way I know how to discuss this is using the proper terms.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What are the grouding requirements for a new 200a service [ 0 Answers ]

It's grounded to the water pipes inside the basement. Do I need a grounding rod (or 2)? My house is in a densely populated part of the city - neighbor's house is ~3ft. Space in between is their property.

Feeder size for 200a sub panel [ 1 Answers ]

What I have is an added 2 car garage with a game room added and connected to the main house. Problem is the main service had to be moved to the exterior of the new garage. I picked up this job after someone else bailed on it. Anyway its been decided to put all the existing circuits into a 200a sub...

Wire size residential service long run [ 2 Answers ]

I need to determine wire size for meter to 200amp panel 900 ft run

What is best way to split a 200A service Entry [ 1 Answers ]

I will be building a summer home over the next three years. I would like to build the garage during the first year, and bring in services. I ultimately will build the house. If I were not going to build in stages, I would have a 200A service in the house with branch circuits feeding the well...


View more questions Search