    Wiring for basement heaters
    I am currently renovating my basement. I plan on running new wiring back to the panel for the basement electric. Since the basement will have an office area and a playroom, I wanted to allow the possibility to have two electric heaters. I plan on using 20 amp rated wiring. Since there is a possibility that both heaters can be operating at the same time, should I dedicate the outlets just for the heaters and run the general purpose outlets on separate circuits or can each room just have the four general purpose outlets together?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jan 20, 2010, 05:52 PM

    You failed to mention some points. It looks like you would like independent thermostats. I think they max out somewhere between 20 and 25 amps.

    I would also assume that your wiring two rooms.

    The maximum wattage for the heaters assuming 240 V is (240)(20)*0.8

    Heating loads are derated 80%. That's the max size for a 20A, 240V breaker.

    Doing the calculations the other way. If you had a 5000 W heater, you would multiply by 1.25 and size the system to (5000)*1.25/240 Amps. The upsize to the next breaker size and figure the wirsize from there.

    Why not use electric baseboard heat it's much safer. Run the power to the thermostat on the wall first.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 21, 2010, 04:00 AM
    Some clarification, proper method of sizing a heat circuit:

    A 5000 watt heater at 240 volts draws 20.84 amps. 5000/240=20.84

    A heat circuit shall be sized 25% higher than the running load.

    20.83 x 1.25= 26.04 amps

    A 30 amp circuit can only handle 24 amps, (30 x .8) so a 5000 watt 240 volt heater will need a 40 amp circuit with #8 copper wire. A 40 amp circuit can handle 32 amps (40 x .8).

    Without knowing the wattage of your heaters, we cannot size your circuits.
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #4

    Jan 21, 2010, 10:47 AM

    I guess I was originally trying to keep it simple by just using portable heaters and used them only when needed. I didn't think about a permanently wired unit with a thermostat. Not that it's not a good option, I just didn't think about it. Since I was just planning on a portable one, I figured it would just be two small units that put out about 1500W at 120V and have their own thermostat. Do you think this is a bad way to go? The room sizes are approx. 140 sf and 250 sf.

    The link to a unit I was considering:

    http://www.homedepot.com/webapp/wcs/...e&ddkey=Search
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Jan 21, 2010, 11:49 AM

    Portable heats should be a temporary solution, not a permanent one. People trip, leave them on. The dog knocks it. It's a fire hazzard. It's bad news all around.

    You claim one of the rooms is an office. With an unregulated temperature, you won't like it.

    The next one is a playroom. If this is for kids, then by all means no!

    It's hard to even guess what you really need in terms of heating, but 25' x 10' is a large space to heat with a small heater unless the basement is insulated very well.
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #6

    Jan 21, 2010, 01:29 PM

    You bring up some interesting points. I will look into maybe the more permanent type and use the numbers you are providing above to calculate the size needed.

    In the past as an office space I have used a single portable unit when needed and it seemed to do the trick since the basement is pretty well insulated. Not knowing the martket that well, can you point me to a manufacture I should look at?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Jan 21, 2010, 02:28 PM
    Kiss is correct, portable heaters are purely temporary. In addition to the issues he brings up, the weak point of any portable heater is the plug inserted into a receptacle.

    This connection will usually heat up, and if used for prolong periods, often the heat created at the plug will damage both the plug and receptacle. Popular cause for fire.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #8

    Jan 21, 2010, 03:29 PM

    I'm not going to recommend or not recommend these,

    http://www.cadetco.com/show_product.php?prodid=1004

    But the website should answer most of your questions. Come back with any questions. These units offer a lifetime element warranty and you may pay more for that.

    Edit: added link
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #9

    Jan 21, 2010, 04:48 PM

    Thanks for the assistance and suggestions. I will do my research and make a determination.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Jan 21, 2010, 05:01 PM

    I'll also say that they make programmable "line voltage thermostats". One example is here: Buy Honeywell Digital LineVoltPro™ 8000 Programmable Heat Only Thermostat | Honeywell TL8230A1003

    Home | Fastenal also has some with a selection tool.
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #11

    Mar 24, 2010, 03:26 PM

    Based on your comments, I have now decided to use electric baseboard heating. Based on the final floor plan, I intend on using:
    (1) - Cadet 3 Ft. 750 Watt 240 Volt Electric Baseboard Heater (3.13 Amps)
    (1) - Cadet 5 Ft. Electric Baseboard 1250 Watt Heater (5.12 Amps)
    (3) - Cadet 4 Ft. Electric Baseboard 1000 Watt Heater (4.17 Amps)

    I will also have three thermostats since this will be three different rooms.

    20.85 x 1.25= 26.06 amps

    So I believe I will need a 40 amp circuit with #8 copper wire.

    Is there any advantage to do one 40 amp circuit vs. two 20 amp circuits?
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #12

    Mar 24, 2010, 05:21 PM
    It depends on how you plan on grouping the heaters just how large of a circuit you will need. You can't just bunch them together. If it was me, I would use three circuits of approproate size. That way each one is protected independently, and the thermostat wiring will be much simpler. If you used just one circuit and one of the heaters shorted, you would have no heat at all.
    Renman521's Avatar
    Renman521 Posts: 24, Reputation: 2
    New Member
     
    #13

    Mar 25, 2010, 07:53 AM

    Thanks for your comments. If I put them on (2) 20-amp circuits, I would break one room that has 12 feet of base board on one circuit and the remain two 4 foot runs would be on the other circuit.

    Based on the math the first circuit would draw (12.51 amps) x (1.25) = 15.63 amps and the second smaller circuit will draw (8.34 amps) x (1.25) = 10.43 amps.

    The wiring for the first circuit is pretty cut and dry since it’s one room and the units are all dedicated to it. I was thinking for the second circuit to run the main feed to a junction box and split off that to the two individual room thermostats then onto the 48” section of baseboard respectively. Do you think this is a problem?

    If I use three individual circuits, I am thinking I would use up all the spare slots in my panel since each breaker would take up two slots.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Baseboard Heaters [ 5 Answers ]

I am wiring two Marley electric baseboard heaters (240v) to a Programmable Thermostat and want to confirm the layout. BASEBOARDS Both Baseboards are 8 feet long, 240 volt, 2000 watt, 8.3 amps WIRE & Circuit BREAKER I am using 12/2 wire and connected to a double pull 20 amp circuit...

Wiring several heaters in line [ 0 Answers ]

I have two 5 foot, and one 4 foot 240V baseboard heaters which I want to slice together along a long wall and run with a 2 pole thermo. How do I wire them to each other?

Wiring Baseboard Heaters? [ 4 Answers ]

I am taking on an electrical project in my basement and I am looking for some guidance, I would like to install 3 basebaord heaters in all. 1 5 footer and 2 3 footers. My question is can I run three on on 2 20amp circuits? Any help would be greatly appreciated.

Wiring 2 baseboard heaters to thermostat [ 1 Answers ]

I recently moved in and the thermostat connected to 2- 2000 watt baseboard heaters shorted out. The burnt out thermostat only had 2 wires, a black and white. Was it the wrong kind? Was it for a single baseboard heater? I purchased a double line dimplex thermostat to replace it. I have 240 VAC....

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...


View more questions Search