    Jonstar's Avatar
    Jonstar Posts: 25, Reputation: 1
    New Member
     
    #1

    Jan 18, 2010, 06:52 PM
    Moving Main Bathroom (drainage related)
    I'm currently in the process of moving our main bathroom from one area of the house to another. Massplumber & Speedball were great to help with a project that I was going to do 2 years ago so I was wondering if I could get a little help on this one! :D

    As with other projects, I will rotate the Drain Tees off center to the vent, etc and make sure there is a 1/4" drop for every foot.

    I'll be running this 3" line from all of this approx 30' to the current waste stack (I'd like to avoid breaking concrete to hook it up).

    How does everything look? Would this vent properly for the shower, toilet and sink?

    I appreciate any and all help! Thanks! :)
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Jan 20, 2010, 06:38 AM
    Hi Jon...

    Can you tell us if WET VENTING is allowed in your area? If it is we may be able to save you some time in terms of the vents.

    If wet venting isn't allowed then you can make the changes I noted below and you will be all set in terms of code... ;)

    Let me know... OK?

    MARK
    Attached Images
     
    Jonstar's Avatar
    Jonstar Posts: 25, Reputation: 1
    New Member
     
    #3

    Jan 20, 2010, 07:24 AM

    Thanks Mark! I appreciate all the help.

    I'm sure code allows wet venting in my area.

    I also assume the long sweep elbows are for better drainage flow (if they're possible to put in - and they should be).

    As for the 2" vent that will hook up to the stack: I did want to ask this question and should have in the first place. There is currently a 1.5" vent running to the stack from in this wall (this room is an old washer/drying room). I figured I would have to replace the 1.5" with 2" to be able to vent the toilet but is it possible to do this with the existing 1.5" vent?

    If replacing the existing vent with 2" is proper and will make sure there are no problems then I will gladly crawl in the attic to make the change.

    Thanks again for the help!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Jan 20, 2010, 07:30 AM
    Code calls for 2" just for the toilet....so a plumber would definitely have to get up in the attic and change it out. With you adding a sink and a shower to this I would definitely increase to 2" all the way... :)

    If wet venting is allowed I can draw up another plan for you if you want, but it will take a couple days... up to you.. OK?

    MARK
    Jonstar's Avatar
    Jonstar Posts: 25, Reputation: 1
    New Member
     
    #5

    Jan 20, 2010, 09:29 AM

    Mark, that would be great! As long as you don't mind! It would save some time and vent pipe so I'm all for it!

    Thanks!

    - Jon
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Jan 22, 2010, 08:05 AM
    Check it out Jon...

    Let me know if it all makes sense.

    MARK
    Attached Images
     
    Jonstar's Avatar
    Jonstar Posts: 25, Reputation: 1
    New Member
     
    #7

    Jan 22, 2010, 08:50 AM
    Thanks Mark. Without over-stating it... You're a God. ;-)

    As for everything you've drawn, I think it will work (though I am trying to work within the 2x10s to so I don't have to bulkhead it down the road - so we'll see how it goes - there is a chance I may have to use the non-wet vent option that you first replied with to make it all fit).

    I've also attached a view of the bathroom showing spacing of lav, toilet and shower. With this spacing in mind, will the vent be enough? I completely forgot to mention how far apart they would be.

    Thanks again for all the help, this project should go off without any hitches given what you've shown me!
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #8

    Jan 22, 2010, 02:41 PM
    That tub can be up to 6-8 feet from the sink vent so you look all set from here!

    MARK
    Jonstar's Avatar
    Jonstar Posts: 25, Reputation: 1
    New Member
     
    #9

    Jan 22, 2010, 04:42 PM

    Great! Thanks again! I'll post here how it goes when I finish it!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom sink drainage instal [ 2 Answers ]

I am a novice at all this plumbing stuff, but am fed up with the lack of quality service I have received so I am venturing into the assembly of my vessel sink. First, the tile guys cut the granite counter wrong and I need to enlarge the holes. Seems that using an alpha core bit on a regular...

I'm looking for a book. Teen. Vampire related, the main character was named Poppy [ 3 Answers ]

Hi. Our town library closed and all of the books were dispursed. I never used to write down the names of the books I had read and now I wish I had. Plot: Poppy and her best friend, I think his name was edward. Friends for years. Poppy is diagnosed with cancer. Then she finds out that "edward"...

Home drainage - cesspit or main [ 2 Answers ]

Who do I contact to find out what type of sewer drainage I have? Or is there another way of finding out?

Possible bathroom/bathtub leak or drainage issue. [ 8 Answers ]

I have a problem in my bathroom, by my tub/shower, but I don't know if it's a leak or what. Here's a little background: Bought the house in June of 2006. Had the bathroom redone entirely (tub surround, vanity, sink, cabinet, plumbing checked, drywall removed and replaced next to tub, drywall...


View more questions Search