    Electrical sub panel
    How is the size of the 240 volt double breaker (the one that protectes the sub panel)at the main panel determined? Exp. Clothes dryer at 240 volts/30 amps-two 20 amp ckt.- one 15 amp ckt. Is it the possible total current draw of 85 amps, if so than the feeder wire will be what size?

    The main panel is located apox. 25 ft. from the sub panel.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 14, 2010, 06:25 AM

    The size of the breaker is determined by the size of the wire.

    The size of the wire is determined by the required feeder size.

    The feeder size is determined by a load calculation, OR the knowledge of an experienced electrician.

    You do NOT add up the breakers to see what the load will be.
    dean1234's Avatar
    dean1234 Posts: 9, Reputation: 1
    New Member
     
    #3

    Jan 14, 2010, 08:22 AM
    Quote Originally Posted by stanfortyman View Post
    The size of the breaker is determined by the size of the wire.

    The size of the wire is determined by the required feeder size.

    The feeder size is determined by a load calculation, OR the knowledge of an experienced electrician.

    You do NOT add up the breakers to see what the load will be.
    How is the load calculation determined?
    14u2c's Avatar
    14u2c Posts: 34, Reputation: 1
    Junior Member
     
    #4

    Jan 19, 2010, 04:52 PM

    Your sub panel should have a rating like 100 amp you need to match the rating of the sub panel feed breaker with the rating of the box.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jan 19, 2010, 05:38 PM
    Quote Originally Posted by 14u2c View Post
    your sub panel should have a rating like 100 amp you need to match the rating of the sub panel feed breaker with the rating of the box.
    Not true at all.
    A 100A panel can be fed with anywhere from a 30A feeder to a 100A feeder.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical Sub-panel [ 1 Answers ]

Running electrical sub panel to pole barn.Does this require 3 conductor service entrance wire with ground ( 2-2-2-4 ser)? Or 2-2-2 seu ?

Electrical panel [ 2 Answers ]

Can I convert an old square d qo panel from a main lug panel to a main switch without doing a service change?

Electrical Panel [ 1 Answers ]

How many watts can go on a circuit that is 2 x 20 = 40 amps?

Electrical panel [ 2 Answers ]

Please give me details of electrical panels-forms1,2,3 as per british standards


View more questions Search