How to add 2 gfci receptacles
Hello, I am wiring my unfinished basement and want to make sure I'm on the right track... I have a 20 amp circuit with 4 recepts on it. The last two recepts need to be gfci recepts because they are within 6 feet of a bar sink. My question is how I need to wire the 3rd and 4th (last on the circuit) do I go to the "line" terminals on the 3rd recept, and leave that recept from the "load terminals? If so, then where do the wires go on the 4th and last recept? To the load side? Please help! Ill be done after this circuit is complete!
|
|
 |
New Member
|
|
Jan 9, 2010, 01:36 PM
|
|
If you install the GFCI as the first outlet on the run and wire the rest of the run off the load side of the GFCI all the outlets on the circuit will be GFCI protected
|
|
 |
New Member
|
|
Jan 9, 2010, 02:03 PM
|
|
 Originally Posted by barr4
If you install the GFCI as the first outlet on the run and wire the rest of the run off the load side of the GFCI all the outlets on the circuit will be GFCI protected
The first 2 are already installed, so can I just hook up the 3rd to the line side, then come off from the load side, then hook up the 4th to the load side?
|
|
 |
Junior Member
|
|
Jan 9, 2010, 02:17 PM
|
|
Generally- If the basement has a concrete slab floor, and the slab is in contact with the earth, all recpts are to be gfi. One gfi at the first box after the panel will do the job. Connect the following recpts to the load terminals of the first gfi.
|
|
 |
Uber Member
|
|
Jan 10, 2010, 05:58 AM
|
|
There is no general about this,
 Originally Posted by johnmprince
Generally- If the basement has a concrete slab floor, and the slab is in contact with the earth, all recpts are to be gfi.
All receptacles located in a UN-finished basement, no matter what type of floor, shall be GFI protected.
|
|
 |
Junior Member
|
|
Jan 10, 2010, 06:16 AM
|
|
Recpt which are considered out of reach, garage door opener on the ceiling or dedicated to and behind a refrig for example, are exempt.
|
|
 |
Uber Member
|
|
Jan 10, 2010, 06:27 AM
|
|
In the National Electric Code 2008 edition, Section 210.8, the allowance of not using a GFI for stationary appliances was removed.
Now, per Section 210.8, ALL receptacles in a unfinished basement and garage must be GFI protected.
ONLY receptacles for fire or burglar alarms are exempt.
John, if you disagree with this, please provide backup to your advice.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
GFCI receptacles in kitchen
[ 1 Answers ]
I am remodeling my kitchen. I have installed boxes for double receptacles. I want to install GFCI receptacles to meet code but I have a question.
1. Can I install 2 GFCIs in series?
2. Do I need too at all? Can I have one GFCI and one normal receptable in the same box and the GFCI protect...
Gfci receptacles
[ 4 Answers ]
Is it possible to install two GfCI Breakers on 3 Wire circuit with a shared neutral. I need to protect the normal receptacles downstream from the GFCI breakers
GFCI and grounded receptacles
[ 2 Answers ]
My home has numerous non-grounded receptacles (2-wire, no ground). Is there such a thing as a whole house GFCI that would make the house safer allowing the convenient use of grounded (3-prong) receptacles?
Also, I thought I read somewhere that if a GFCI is placed as the first receptacle that...
Can a hood be on the same 20A circuit with already 2 duplex GFCI receptacles
[ 3 Answers ]
In my kitchen I have 2 duplex GFCI receptacles above the countertop on one 20A circuit.
I cannot pull an extra wire through the existing conduit so would like to hook up the hood and the range (all gas but needs power for the electronics) on that same circuit.
Does the NEC 2005 code allow for...
15A receptacles on 12/2 GFCI Circuit
[ 5 Answers ]
I was just looking at some of the wiring that was done in my house when it was built in 2003. I have one GFCI Circuit that has 5 receptacles on it. On this, it is wired all with 12/2 to the garage first, where the receptacle is the GFI, then it runs 3 outdoor receptacles, and 1 in the basement. ...
View more questions
Search
|