    Switching from a gas hot water heater to an electric model.
    Would like to run an electric circuit from 200 amp main panel to a new 100 amp sub-panel in the attic.

    Need 220volts @ 30 amps for hw heater, and would like to provide electrical capacity for eventual finishing of attic as bedroom and office.

    The circuit run is about 25' from main panel. Was planning on using #4 copper.

    Can I use a 60 amp breaker in the main panel? Should I consider anything else?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 8, 2010, 01:46 PM
    Yes, you can use a 60 amp breaker to supply the 100 amp panel in the attic, using the #4 conductors.

    The feeder will need 3- #4 for the two hots and one neutral, and min 1 -# 10 fr the equipment ground.

    The neutral bar will need to be insulated and isolated from any equipmet grounds.

    The #10 will need to connect to a separate equipment ground bar bolted directly to the metal panel box with machine screws, and only be for bare or green equipment grounding conductors.

    60 amp is a bit light, at least 26 amps will be used for the heater. Is 60 amps enough for the total future load?

    I caution you about putting a bedroom in an attic. Building and fire codes require two egress (exits) in the event of a fire. You will learn this when you apply for building permits.

    Smoke detectors will be needed, no matter if a bedroom exists or not.


    Best I can think of what you need to consider.
    johnmprince's Avatar
    johnmprince Posts: 56, Reputation: 4
    Junior Member
     
    #3

    Jan 9, 2010, 05:36 PM

    Is access now through a code legal stairway? If not you may find it tricky to add one without killing a lot of space on the floor below. I've been there.
    A 60 amp panel will give you 14,400 watts of use. A hot water heater is usually 4,500 watts. If you use electric heat, then two 8 foot heaters, one for each room, total 4,000 watts, leaving you with nearly 6,000 watts for everything else. This is a lot, a whole lot.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No water in hot or cold bathroom sink after flushing my gas hot water heater [ 5 Answers ]

Thank you. I flushed my hot water heater last night. I only turned the cold water intake to the heater off and on BUT now, after the flush, my second floor bathroom sink faucets (both hot and cold) don't work at all. The shower and the tub in the bathroom work but NOT the sink- HELP! Thanks so...

I have very low hot water pressure from my hot water heafrom an electric water heater [ 0 Answers ]

I have very low water pressure from my hot water heater. I can't find anything wrong.. any ideas?

Electric start gas hot water heater [ 2 Answers ]

This is a gas hotwater heater with an electric ignition. It states it is not to be lit manually. It lites on demand for hot water and it is trying to lite but will not catch. I have read that it could be a faulty therm coupler. There is gas supply to the rest of the house, heater is 4 to 5...

Electric or gas tankless water heater? [ 1 Answers ]

I am in the process of building a new home. I have 3 children and want to go as energy and cost efficient as possible. So, here's my question: Should I go with an electric or tankless water heater? Or should I go with a high energy efficient regular electric water heater? Everything in the...

Replaced electric water heater Atlanta area, but no hot water [ 14 Answers ]

The old water heater died. Bot one (38 gals) at HD. Installed exactly like the old one was as follows--3 CPVC pipes come out of wall. Two are joined. Before they are joined one has a valve. After they are joined there is a second valve. The pipe is connected to the cold side of the heater using...


View more questions Search