    Carrier 58GS100-GA Series 160, about 1986/87 vintage
    Replaced thermostat as well as the thermometer wire. Heat turns on if I shut down thermostat, gas, electric, and fuse then turn them back on in the following order: 1. fuse 2.gas, 3. electric switch to the furnace, and 4 thermostat. It shuts down after a couple of minutes. I am a single parent on a limited budget and do not feel like going this procedure to raise the house temp from 56 to 57... Help! Thank you for your suggestions!!
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Dec 10, 2009, 07:09 PM

    I think that system has a 3 wire pilot assembly on it. Will the burners ignite and burn.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Dec 11, 2009, 12:46 AM
    If you have one of these tap on it with a screwdriver or other tool. This may get it working for a time or two. If not I would still suspect the 3 wire pilot as T-Top mentioned.
    Attached Images
     
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Dec 11, 2009, 04:10 AM
    The thermostat could be the problem. Try this: turn off power to furnace, remove thermostat wires "R" & "W" and connect together. Turn power back on and observe. If furnace sustains operation, the thermostat is the problem. If not, at least it has been eliminated from contention for blame.
    Attached Images
     
    freezingcold's Avatar
    freezingcold Posts: 5, Reputation: 1
    New Member
     
    #5

    Dec 12, 2009, 12:12 PM

    First of all, Thank all of you who replied to my post, and I know a whimpy californian shouldn't be complaining about 45 and rain when I saw how cold it was in Ohio this week.
    Reply in regards to the first 2 replies.
    I do have a three wire pilot that stays lit after I go through my progression of: fuse, gas, electric, thermostat to get the heat to function for a couple minutes. The pilot lights almost immediately followed a minute or so by the burners then finally the blower turns on. The burners turn off first then the blower turns off next; however the pilot light stays lit.

    Reply to post 3
    I have powered down and connected the R&W wires together, and the furnace functions exactly as described above which I guess means my thermometer is the culprit?
    I have tried 3 different thermostats after getting rid of the old mercury one.
    Models are all 5-2 programmable
    Rite temp model 6022
    Honeywell rth2310b
    Honeywell rth2309
    Is my ancient furnace to old for one of these thermostats? Or could it still be the pilot?

    Thank you very much
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Dec 12, 2009, 01:17 PM
    Actually on the three wire pilot style the pilot usually goes out when the furnace shuts down and relights on a call for heat. Why your is staying on is a good question since those pilots have spark or on the real old one glow coil ignition.
    freezingcold's Avatar
    freezingcold Posts: 5, Reputation: 1
    New Member
     
    #7

    Dec 12, 2009, 01:58 PM

    Thanks again for your continued support. A few things I've observed about the pilot light with all models of thermostats mentioned above: when I switch the thermostat to off the pilot light slowly goes out. When I switch the heat back on after 5 or so minutes the pilot lights up and the furnace goes through one cycle and the pilot stays on until I either turn the gas off or switch the thermostat off. Also, I hear a quick loud squeek when the burners shut down, I imagine this is some kind of valve in desperate need of some lubrication. When the burners light no squeek upon firing up. I'm going to look up the pilot light's part number (probably after market version) and replace it. If anyone knows the part number off the top of their head, please let me know.
    Thanks and have a great day
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #8

    Dec 12, 2009, 07:22 PM
    If the pilot switch hot contact circuit opens during a heating demand, it will cause exactly what you are experiencing. This circuit not only powers the main gas control, but also initiates the blower timing control circuit. Part # LH680005.
    Attached Images
     
    freezingcold's Avatar
    freezingcold Posts: 5, Reputation: 1
    New Member
     
    #9

    Dec 12, 2009, 08:22 PM

    I've ordered the part. I will let you know what happens upon installation. Thank you again for all of your assistance, Merry Christmas or Happy Holidays for all of you PC folks.
    Peace.
    freezingcold's Avatar
    freezingcold Posts: 5, Reputation: 1
    New Member
     
    #10

    Dec 20, 2009, 07:50 PM

    The pilot light assembly was the answer! I received and replaced the part. She fired up and kept the temperature at 68. I brought the first progamable thermostat out of the doghouse and back into full service. Returning the other two. Thank you for all of your assistance, I could not have tamed the beast without your help!
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #11

    Dec 20, 2009, 09:10 PM

    Does this mean you'll be changing your name?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hvac carrier 58gs100-2 no heat no blower [ 1 Answers ]

I have a carrier model 58gs100-2. The tstat works and the pilot light when tstat is turned to heat, but nothing else happens, no other flames and no blower!! Please help!!

Carrier Vintage gas furnace [ 0 Answers ]

Standing pilot gas valve model Vr8200H1228, found "X" terminal to valve, conductor on othe terminal disconnected from control board, NO pilot, no nothing. What location would the other conductor be replaced, 24v trans normal terminal points X R B Y W any place to get older Carrier wiring diagrams?...

Carrier model 58GS100-GB furnace will not ignite [ 1 Answers ]

Ignition lockout module ----can not find part

1986 Carrier Rooftop [ 1 Answers ]

Yes, I know I should probably just change the system but the AC works great still and I just want to make it through this winter. If there is a quick fix please let me know. Both the fan and the A/C work, however, when I switch the unit over to heat there is nothing. The thermostat is one of...

Carrier 58GS100-2 201BB [ 1 Answers ]

The blower motor (which is brand new 1/2hp) will not start unless I turn it by hand. It appears to be the capacitor, but I have no idea what the capacitor looks like or where it is located. Can anyone help please. Much thanks


View more questions Search