    Help I have a boiler that I think is air locked
    I have a baseboard oil fired hot water boiler that I have just finished and the boiler fires OK however I am not getting heat anywhere in my home the supply pipe is hot up to the first 90 above the boiler and cold after that can anyone please help me out
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 7, 2009, 12:22 AM
    Low water pressure in system. In active pump.
    banditmc's Avatar
    banditmc Posts: 7, Reputation: 1
    New Member
     
    #3

    Dec 7, 2009, 02:56 PM
    No I have good pressure and circulator is working boiler gets up to about 40 lbs
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 7, 2009, 04:27 PM
    40 PSI ? Is this a residential boiler in the USA.

    Brand of boiler and Exact model number?
    banditmc's Avatar
    banditmc Posts: 7, Reputation: 1
    New Member
     
    #5

    Dec 7, 2009, 04:32 PM

    Dunkirk empire II model number 3ew.75z yes in New York state
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Dec 7, 2009, 04:34 PM

    40 lbs is way to high, your pressure relief valve should be blowing off at thirty psi. You should only have between 12 and (at most) 25 psi. You said you just got done installing the boiler. Did you purge the lines and bleed all registers? Sounds like and air lock problem. Double check that pressure reading and let me know if its really at forty. If it is, shut the unit down and have a pro in to look at the system.
    banditmc's Avatar
    banditmc Posts: 7, Reputation: 1
    New Member
     
    #7

    Dec 7, 2009, 04:39 PM

    I checked the gauge on the front of the boiler and it reads 40 the blow off valve isn't opening on the back of the boiler though could I have a bad gauge
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Dec 7, 2009, 04:47 PM
    Here is a link to your new boiler. All information you need is included in the downloads to the right. They make a good boiler and I believe your lack of experience is causing your problems. I suggest like mygirlsdad said that you contact a professional ON SITE service person to sort all your problems out. You can create a bomb out of this boiler if you are not careful since the safety must be plugged or not installed for this boiler to reach 40 psi. My concern is for your safety as well as for the safety of others in the building.

    Empire II Water Series Boiler For Sale at Dunkirk
    banditmc's Avatar
    banditmc Posts: 7, Reputation: 1
    New Member
     
    #9

    Dec 7, 2009, 05:43 PM

    One last question if I may does it make a difference if I have a radiator and baseboards in this system together
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Dec 7, 2009, 06:47 PM
    It could but that really depends upon who engineered the system. Pipe restrictions can caue problems with flow and your system should have automatic ventors on it at least at the high point of the system.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Not a strong air flow coming from my air vents [ 1 Answers ]

I have a problem with my air flow - I have to turn the temp. on the thremostat all the way up or all the way down to to get the house cool or heated. Even with that, I do not feel a strong breeze coming from any of my vents in the ceiling. I have an upstairs unit and a downstairs unit and both give...

Two-zone EWC-ST-2D gas hot air and air conditioning furnace [ 0 Answers ]

I have a two-zone EWC-ST-2D gas hot air and air conditioning furnace. With two RITETEMP 8050 thermostat controls mail level and the other is upstairs. Is the C wire the other side of the 24VAC heating transformer because the 8050 can run on 24VAC series power. 24VAC ONLY. Power for the...

Air solvents [ 1 Answers ]

What are the other substances that can dissolve air apart from water.

WR 1F95-391 w/ central air + HW Boiler [ 1 Answers ]

Right now my heat is connected to an older thermostat. When I had my Central Air installed I never combined thermostats. Now my heat thermostat is on the fritz and I would like to use the WR thermostat for both. Can this be done? I only see one set of 24V terminals, you can't terminate them both on...

Connecting a wood boiler to exsisting boiler [ 2 Answers ]

I need a plumbing diagram to connect a wood burning boiler to an exsisting primary boiler, exsisting boiler is apeerless 105/85 that is approx. 20 years old


View more questions Search