    Furnace line voltage polarity reversed
    I recently turned on my heater for the first time. The fan is blowing, but there is not hot air. I went into the attic and reset the ignitor switch and still no luck. The green light in front of the furnace is blinking ten times, indicating the line voltage polarity is reversed. What should my next step be in making this furnace work.

    The furnace was recently put in before buying my home.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 6, 2009, 05:28 PM
    The furnace was recently put in before buying my home

    If the furnace is new or close to new call the contractor that installed it since it will be under warranty.

    If not use a meter and start checking for reverse polarity OR if that is not the case reverse the 24 volt low vlotage leeds going to the board.
    AnthonyIOSOS's Avatar
    AnthonyIOSOS Posts: 4, Reputation: 1
    New Member
     
    #3

    Dec 6, 2009, 06:26 PM
    Quote Originally Posted by hvac1000 View Post
    The furnace was recently put in before buying my home

    If the furnace is new or close to new call the contractor that installed it since it will be under warrenty.

    If not use a meter and start checking for reverse polarity OR if that is not the case reverse the 24 volt low vlotage leeds going to the board.
    Is reversing the 24 low voltage leads safe to do? I will unplug the unit, reverse the leads and turn the unit back on. I just want to make sure if leads were reversed incorrectly that it would not cause any electrical explosions or fires.
    AnthonyIOSOS's Avatar
    AnthonyIOSOS Posts: 4, Reputation: 1
    New Member
     
    #4

    Dec 6, 2009, 06:27 PM

    Also if I got a meter and tested for reverse polarity what would be my next step?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 6, 2009, 06:48 PM
    First you need to reverse the leeds and try the unit. Yes it is safe to reverse the 24 volt leeds.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Dec 6, 2009, 07:01 PM

    A meter would be tough. They say revered polarity, but it's really phase reversal.

    The 24 VAC peak must coincide with the 120 VAC peak which would be difficult to detect.

    Polarity reversal interferes with the flame detection circuitry.
    AnthonyIOSOS's Avatar
    AnthonyIOSOS Posts: 4, Reputation: 1
    New Member
     
    #7

    Dec 9, 2009, 09:58 AM
    Quote Originally Posted by hvac1000 View Post
    First you need to reverse the leeds and try the unit. Yes it is safe to reverse the 24 volt leeds.
    Thanks for all the help. I contacted the people who sold the home and those people contacted the company that installed the heater. The heating company came out and reversed the leads for me. Heater is up and running!

    Next project fix the broken sprinkler head...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Live Voltage Polarity Reversed [ 2 Answers ]

I just installed a new circuit board in my Carrier furance. When I do the Self Test I get a rapid flashing light which indicates a line voltage polarity reversed issue. How do I correct? Which color wire should be connected to the Com 24 connection? Thanks

Goodman furnace reversed 115 vac polarity [ 2 Answers ]

I have a 3 yr old goodman furnace and went to turn it on for the first time this yr last night it turns on and runs for about 10 sec. and turns off it does not light. The troubleshoot light blinks continuously which on the sheet says reversed 115 vac polarity whatever that means. I hope its...

What is reversed polarity [ 1 Answers ]

What is reversed polarity

Reversed polarity [ 3 Answers ]

What does reversed polarity mean a. the hot and neutral are wired forwards b. the ground and neutral are wired backwards c. the hot and neutral are wired backwards

Reversed Polarity [ 1 Answers ]

Regarding reverse polarity, I have 5 outlets in a room all showing reversed. The top of the outlets are wired to the light switch(red wire) the bottoms are hot all the time(black wire). When I remove the red wire from the switch the polarity is fixed.. if I hook that wire back up they then reverse...


View more questions Search