    Using 20 amp plug on 15 amp outlet
    I am buying a dry sauna that has a 20-amp plug. The outlet in my home says 15A. The breaker for this outlet says 20. Can I use this dry sauna on this outlet. Do I need to change the outlet. Is breaker adequate if I do this? Dry sauna brochure says: 120 volt / 1531 watt/ 12.75 amp. If I change anything, is it possible I need a permit from the city? Thanks.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 17, 2009, 11:13 AM

    I suggest that you place the Sauna on an dedicated 20 amp circuit.

    This means that the breaker needs to be a 20 amp breaker. The cable from the breaker to the outlet receptacle must be 12/2 AWG for copper.

    The receptacle should be a 20 amp receptacle.

    As to the permit, a simple phone call to the LAHJ (electrical inspectors) can get you that answer.

    One major concern that I have is that someone may have installed a 20 amp breaker where a 15 amp breaker had been installed. If that happened and the cable was not upgraded to 12/2 AWG then you may well have a fire hazard inside your wall.

    A 14/2 AWG cable is not allowed to be used on a 20 amp circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My Life everything within it around it & myself [ 8 Answers ]

My Life really not getting on that too much not enough room beyond that its has been nothing but confusion depression sadness pain more more more & more. However for some reason still here not for sure how much longer just as the next however with other info. Finding out and thing I do and have...

B&s [ 1 Answers ]

I have a b7S model 243431-0123-99 I need to khow what to set the points on. Thanks

Amp breakers [ 7 Answers ]

I found my mom's submersible pump wired to a two single pole 20amp breakers and there is a double pole 30amp breaker on the bus panel as well. I already know that all 220volt leads need to be on a double pole breaker in case one leg grounds out. So I switch the wires over to the double pole 30amp...

IUD & Update [ 10 Answers ]

I need some information on the IUD. I am having it put in three weeks and I want some information on it, I have Google it But you know how it is to find good information, Wondering if anyone knows a good site. Banner doing well. Still gettting use to having Two kids at a time, it's...

Where to Buy Rod & Key to Turn On & Off Old Gas Floor Heater [ 0 Answers ]

Where do I purchase a rod and key to turn on and off an old gas floor heater?


View more questions Search