    Back to back washer/dryer
    see attached picture

    putting in two sets of washer dryers on the opposite sides of one wall (2x4).

    I have an existing 2" drain coming out of concrete floor, everything else is planned

    i plan to put a clean out near floor followed by a sanitary cross branching out with a 2" vent to basement ceiling vented to side of house.

    My questions:

    (1)
    Will the 2" drain line be capable of draining 2 washers? The books i've seen list the fixture unit FU of a washer at 2, with a total of 4 for the 2 washers. The listed max FU of a verticle 2" pipe is listed as 10 and the max FU of a horizontal 2" pipe is 6. The 2" pipe coming out of floor changes to a 3" by a 3/2 bushing below the slab before it goes horizontal, so there is never a horizontal 2" segment of pipe carrying double capacity. The 3" pipe was not carried up the wall because it is 2x4.

    [QUESTIONS 2&3 might need to be asked in another forum]
    (2)
    Being a 2x4 wall, a 4" dryer vent will not fit. I plan on running 3" dryer vent to ceiling and transitioning to 4", for each dryer seperately. Is this unsafe to have an approximately 6 ft. section of 3" vent pipe for each dryer or merely not ideal. Worst case I could use 2x2 lumber to widen the wall to allow 4" dryer vent.

    (3)
    I have to have the washer/dryer on the right stacked. How is this laid out? Dryer is ontop of washer right? Not sure of height requirements.

    Please correct me, typically 120V washer outlet is higher than washer box in case of leaks. And the dryer vent and 240v would be higher than the washer box in a stacked setup.
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #2

    Nov 16, 2009, 11:21 AM
    Hi Rage...

    1) You will be fine with the 2" pipe. Although, FU count is probably closer to 6 FU as these washing machines will have a 2" waste line. You should still be just fine with that 3" below the floor.

    2) Widen the wall with the 2"x2"... do NOT reduce the dryer vent in any way. Clothes will take longer to dry, lint will build up quicker and is not recommended by the manufacturer. Adding a cleanout tee with a cap in each dryer line will help you to vacuum the dryer lines out in the future... especially as they go vertical.

    3) Dryer is on top. The 240V electrical box for the dryer and the 120V for the washer should be at a height just above the washing machine.

    Good luck...

    MARK
    ragedriven's Avatar
    ragedriven Posts: 8, Reputation: 1
    New Member
     
    #3

    Nov 16, 2009, 04:45 PM

    I have had someone else tell me to tear up the concrete and continue the vertical 3" pipe up through wall and widen wall using 2x2.

    or use a #5 fittings (whats a #5 fitting?)
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Nov 17, 2009, 05:46 AM
    Well now... that is a problem now and then... different code books dictate different acceptable standards.

    At this point I can only advise you to call your local plumbing inspector (or the next town over... ;)) and just ask him what he would accept... only way to get most correct answer for you.

    Let me know what he says... O.K.?

    MARK

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Diagram of back of washer? [ 3 Answers ]

My Kenmore washer does not kick into the rinse cycle and I have to bang the door shut to get it to switch. Weird, huh, but my only resolve. I do not have an owners manual for my Kenmore washer because it is a reburbished washer with a whirpool tub. And the store went out of business of...

Washer causes sewage to back-up [ 1 Answers ]

Hi, I am not mechanically inclined AT ALL. I rent a house where my land lord is not good at keeping up repairs, and blames me when she does. When I run my clothes washer, sewage comes up through the tub and toilet. The 2 sinks in the same bath and separate shower stall in same bath gurgle. The...

Washer back flow [ 1 Answers ]

Our washer is overflowing from the drain pipe into the basement, what could this be? The toilets, shower or sinks do don't back up. Only the washer after 3-4 loads?

Washer back up - not a clog! [ 4 Answers ]

Our basement floor drain began backing up after washing several loads of laundry in a row. Our plumber explained that there was a clog in the line between this drain and the street but since there wasn’t a cleanout, they would need to dig up the floor and place one in the line. After the cleanout...

Washer back up into sink [ 2 Answers ]

:confused: When the washing machine drains it backs up into the kitchen sink which is about ten feet away then drains out. This sink drains very slowly, if I plung it once or twice it drains fast.


View more questions Search