    Trying to Install 2 Motions Sensors in One Circuit
    I'm looking to have two Motion Sensor on one circuit. Long walk and want one sensor at both ends.

    The Sensor I'm using:
    http://rikain.com/Manuals/Intruder_a...nteck/ES34.pdf

    Also Note the Sensor I'm using allows you to switch it 'off' and 'on' quickly in order to override the sensor and have it stay on for a period.

    The following is the circuit I'm looking to build:
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 10, 2009, 08:11 AM

    The short red vertical wire at the box (box where wires meet) needs to be removed.
    bbriggs's Avatar
    bbriggs Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 11, 2009, 07:39 AM
    Quote Originally Posted by KeepItSimpleStupid View Post
    The short red vertical wire at the box (box where wires meet) needs to be removed.

    KeepItSimpleStupid, Thanks. Maybe my drawing is confusing but I assume I need to have all wires in the LS channel connected to allow all lights to be turned on by either sensor. Otherwise if I remove that connection the lights will be operated independently.

    Assume that vertical line just means the wire terminate at that point. If I leave that connection as drawn will the circuits work?

    Thanks again, BBriggs
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Nov 11, 2009, 10:06 AM

    Your right. Sorry. The drawing is confusing. The two gold verticle lines heading downward probably should have been red.

    Using black (hot), White ( a tough one) and RED (Switched hot) which are the same wires in the cable would have helped too. These are the same colors in say typical 14/3 cable.

    Looks OK.

    If your really unsure, you can breadbord it up with 2 detectors and 1 light and one of my famous "killmequicks". It would not be unusual for me to do something like stuff wires into an extension cord to get simple power for a test spread out on the floor.

    Light bulbs in SERIES with the power make great current dependent resistors. So a 100 W bulb in series with your power switch and a night light load will basically say your circuit if shorted can draw no more than 100 W.

    The cold resistance of a lamp is about 10-15 times less then the resistance when hot. That's why it works. You mst have minimum loads if the motion detector using a solid state switch.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to add two motion sensors to existing light circuit? [ 14 Answers ]

I have a circuit with a single switch connected to four outdoor lights. I would like to add two motion sensors so that either of them will trigger the lights to go on. Can someone please help me with suggestions and/or a wiring diagram? The motion sensors I have are like this one: Link. They...

Circuit breaker trip after install of GFCI breaker [ 3 Answers ]

I'm replacing an outlet under kitchen sink that garbage disposer and dish washer were plugged into because they stopped working. The old outlet was not GFCI. So I'm attempting to replace it with one. Our home was built in the '50s and has no ground line yet. I used an extension cord to plug them...

How to install motion sensors to exsisting recessed lights [ 2 Answers ]

Can anyone help me, I want to install a motion sensor unit to my front porch lights.. which Are recessed lights. I have unscrewed the unit and found there are 3 white cables I see two cables runs directly to the recessed main box while the other one I have no idea I'm guessing that...

Going through the motions? [ 3 Answers ]

What does it mean for someone to be going through the motions in a relationship? Especially one that's been going on for a little over a year? My friend has been dating a girl for over a year and I always assumed he was happy because of Facebook comments the girl leaves and from an outsiders...

Install 240 circuit breaker [ 1 Answers ]

I just install circuit breaker 240 v ,but when I use the meter it can only read 120 v on each pole when I check both pole I don't see any thing in the meter,:eek: why is this happen Thanks


View more questions Search