Installation of programmable thermostat
I've just bought a new programmable thermostat. In the installation guide, it says "The wires are usually designated W, Y, G, RH, RC, O, B, H1, H2."
But, in mine, a Coleman system, they are designated as W2, Y, G, O, B, L, E, X, R. How should I make them match?
Thanks!
|
|
 |
Ultra Member
|
|
Nov 6, 2009, 07:47 PM
|
|
Are there more terminals on the new stat other then the ones you have listed?
|
|
 |
New Member
|
|
Nov 6, 2009, 07:48 PM
|
|
Nope, that's all I have
|
|
 |
Ultra Member
|
|
Nov 6, 2009, 07:51 PM
|
|
What does the instructions say the h1, and h2 are for?
|
|
 |
New Member
|
|
Nov 6, 2009, 07:54 PM
|
|
H1 and H2 are for an humidifier... But, I don't think my system is equipped with an humidifier
|
|
 |
Ultra Member
|
|
Nov 6, 2009, 07:57 PM
|
|
Does this new stat say it will work for 2 heat 1 cool? Or just 1 heat 1 cool with heatpump?
|
|
 |
New Member
|
|
Nov 6, 2009, 08:05 PM
|
|
It says:
- automatic heating or air conditioning control
- for central heating systems
- 5+1+1 day programmable thermostat
|
|
 |
Ultra Member
|
|
Nov 6, 2009, 08:08 PM
|
|
Inless it says 2 heat it will probably not work for you. You will have to get a 2 heat stat to get your electric furnace and heatpump to both work
|
|
 |
New Member
|
|
Nov 6, 2009, 08:12 PM
|
|
Ok, so I will put everything back in the box and go back to the store!
|
|
 |
Uber Member
|
|
Nov 6, 2009, 08:25 PM
|
|
Your new stat doesn't have the ability to set the furnace to Emergency Heat - The E terminal is missing
X is probably (C) or common which is sometimes used. Not used if the thermostat is powered by batteries alone.
L is an indicator - has various uses, not needed.
Ususllay you have O/B not O and B. SOme zoning controls require both. It's rare to find them. You generally program how O/B behaves. It usually goes to the reversing valve.
On the new stat Rc gets conncted to Rh and it becomes R.
H1 and H2 is a dry contact for a humidifier.
W could connect to W2
Biggest problem your missing E. E forces the heat pump off and uses the strip heaters alone. Make sure you need both O & B.
Wrong stat. You need one with Emergency heat.
|
|
 |
New Member
|
|
Nov 12, 2009, 04:17 PM
|
|
I finally bought a new thermostat that should be oki. But I still have one last problem:
Wires existing on my old system : W2 ; Y ; G ; O ; B ; L ; E ; X ; R
Wiring suggested: W2 - Aux ; Y - Y ; G - G ; O - O/B ; B - C ; L - L ; E - E ; X - (C or E, already used!); R - R
So, I have a problem with my X!
The only other plugs available are RC and Y2.
"KeepItSimpleStupid" wrote : "X is probably (C) or common which is sometimes used. Not used if the thermostat is powered by batteries alone."
- That means that if I use batteries, I can use just without wiring it?
Thanks!
|
|
 |
Uber Member
|
|
Nov 12, 2009, 05:20 PM
|
|
Yep. Is your unit a Trane by chance?
You also need to jumper Rc to R and possibly Y2 to Y on the thermostat. Rc to R is a necessity, otherwise the fan and AC won't work.
|
|
 |
New Member
|
|
Nov 13, 2009, 07:02 AM
|
|
My new thermostat is a Honeywell.
The jumper between Rc and R is already there, but not between y2 and y and there is no mention about it in the instructions.
|
|
 |
Uber Member
|
|
Nov 13, 2009, 08:02 AM
|
|
You didn't mention the model of the thermostat. Y2 is second stage cool. If you can set the tsat to 1 stage cooling, that would be best.
I believe Y2, unconnected will be fine.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Replacing thermostat with programmable thermostat
[ 1 Answers ]
I just bought a Robertshaw 9600 programmable thermostat to replace Robertshaw 9500.
My old thermostat ( Robertshaw 9500 ) has R, W, Y, B , O , G with R(ed) connected to RC and others connected to their corresponding colors.
New Thermostat has only RH, RC, W,Y,G. There is no room to connect...
New programmable thermostat installation
[ 0 Answers ]
Hi to all,
Hope anyone can lean me a hand on my installation for a new programmable thermostat.. I got old 3att86 model thermostat which I'm about to replace with lux touchscreen tx9000ts.
The wire with old 1 are labelled ( Y, G , R, O, W2, E and C) while my new has (W,Y,G,B,O,RC,RH and C). Im...
Programmable themostat installation
[ 1 Answers ]
I am in the process of changing over to a Programmable Thermostat and wanted to have some guidance on the wiring on the new thermostat.
Old themostat:
White-Rogers Heat Pump Thermostat 2H/1C, Type 1F59-11
Current wiring at this thermostat:
Horizontal wires:
W- white wire
R- red wire
L- no...
Programmable thermostat
[ 1 Answers ]