    Upgrade service and plan for future duplex/motherinlaw apartment
    Have an older home with 100 amp service; 2500 square feet in a U-shaped footprint. Need to replace ancient HVAC system and also plan for future splitting of home into a duplex. City and fire marshall requires one meter when there is no firewall until zoned as duplex. Eventually, all will be electric, two kitchens, heat-pump with strips. Do I need a 300-400 amp service, or what size will eliminate having to do this again? If using a bigger amp service, can I set up two main breaker boxes with 200 amp for the expected three bedroom unit and 100 amp for 1 bedroom unit? Trying to keep costs down and yet plan for future when 2 car garage would be converted into two bedrooms and a laundry room. Suggestions are appreciated.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 8, 2009, 05:26 AM

    A residential 400 amp service can be installed, called a 320 amp service. This can feed two 200 amp panels, or one 200 and one 100 if so desired.

    If this size is correct is is unknown until a service calculation is done. This needs to be done by an electrician, and the final outcome will depend on the square footage of livable space, and a list of all major electric appliances, air conditioning, electric heat.

    If you can provide all of this detail, we can do the calcs here.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Using AT&T Tilt as tether for PC w/o plan upgrade [ 1 Answers ]

I have broadband on my AT&T Tilt, but it costs extra to get a plan to use it to tether a laptop or PC. Since my broadband is unlimited, why should it matter if I hook up a laptop with a USB cable? Will it work without upgrading my plan? Is there a work-around?

3rd floor apartment electric upgrade [ 10 Answers ]

I'm thinking of re-wiring our third floor apartment. This will probably amount to: 5 x main light switches 8 x duplex outlets 3 x GFI's 1 x 20 amp outlet for an airconditioner. the old wire is knob and tube and is keeping me a wake at night... FIRE! I have a 100 amp panel dedicated to this...

200 AMP Service Upgrade [ 4 Answers ]

I am in the process of upgrading my main breaker panel, I was wondering if someone can advised me on some of the thing that I should ensure that the electrician list on the proposal as part of the upgrade. For instance, I see 200 AMP aluminium wire, new#2 copper grounding wire conductor, new#4 or...

200 Amp Service upgrade [ 3 Answers ]

Good afternoon, Here's the scenario: I picked up a house that was in the middle of a remodel. Seeing a new 200 Amp breaker box, I dug around and found the old breaker box was a 100 Amp. The wires entering the house have not been replaced, as in they are too small, 2/0. I went out to the meter...

Fire Damage to Apartment - Landlord using to upgrade apartment [ 8 Answers ]

Earlier this year my apartment was minimally damaged by a fire. The exact cause of the fire is unknown, however it is believed that my cat knocked something onto the stove which then turned on and burned the basket. Fire damage to the apartment was restricted to the kitchen stove area. Smoke...


View more questions Search