    200 AMP Service Upgrade
    I am in the process of upgrading my main breaker panel, I was wondering if someone can advised me on some of the thing that I should ensure that the electrician list on the proposal as part of the upgrade. For instance, I see 200 AMP aluminium wire, new#2 copper grounding wire conductor, new#4 or 6 copper grounded conductorfinally AL SEU service cable are these thing necessary or are there anything else missing?

    Your help is very much appreciated,
    Fred
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 19, 2007, 11:35 AM
    Can you clarify your question? Are you looking to add something to the proposal? Or are you trying to understand the quote and be sure something is not missing?

    Even if the quote lists something specifc how would you know it is there or not?

    The service entrance cable should be #4/0 aluminum SER cable from meter to the panel. This cable includes the equipment grounding wire.

    What is the copper #2, #4, and # 6 for? Only # 6 is required if this is the grounding electrode conductor, the wire that connects from the main neutral to the ground rod(s) or city water.

    If you want to proposal reviewed, can you scan and post it here?
    tallnblk's Avatar
    tallnblk Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 19, 2007, 12:57 PM
    Thanks TK,

    For your help, I wanted to see if someone who is familiar with upgrading a main panel breaker from 150 AMP to a 200AMP. I was hoping this person would be able to inform me as to some of the basic things that needs to be done in order to meet the NEC.
    BTA's Avatar
    BTA Posts: 15, Reputation: 2
    New Member
     
    #4

    Apr 19, 2007, 02:43 PM
    Tkrussel:

    Only #6? Really? I'm not familiar with the NEC but I find this interesting as the CEC (Canadian Electrical Code) would require a mininum #3AWG Cu grounding conductor for a 200A service conductor.

    ... again, I'm not familiar so the requirement may be different but that seems small to me...
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Apr 20, 2007, 03:01 AM
    Per the NEC Section 250.66 (A) when the conductor is solely for the connection to a rod, plate or pipe electrode, the minimum size allowed is #6 copper. If to building steel, a ground ring, a city water line, then the grounding electrode conductor is sized according to the size of the ungrounded service entrance conductor, per Table 250.66.

    So it starts with #2, which is typical for a 100 amp, #8 is allowed.

    Yes I understand there are some significant differences between the NEC and the CEC. I would love to find a copy to learn from.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

200 Amp service upgrade help. [ 15 Answers ]

I am planning on upgrading my existing service from 125 AMP to 200 AMP. This is in a new house (3.5 years old). I am doing this because I am adding a pool and extension that will require a fair amount of power (60-80 AMP's). I also plan on adding some circuits for woodworking, etc. The existing...

200 Amp Service upgrade [ 3 Answers ]

Good afternoon, Here's the scenario: I picked up a house that was in the middle of a remodel. Seeing a new 200 Amp breaker box, I dug around and found the old breaker box was a 100 Amp. The wires entering the house have not been replaced, as in they are too small, 2/0. I went out to the meter...

Home Electric service 200 amp upgrade [ 2 Answers ]

I need to upgrade my current 100 amp service with fuses, to a new 200 amp service Box. What would the total ball park price be including labor, and material. Thanks,

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search