    thermostat for a 2 stage hi-eff furnace
    I have a conventional furnace running on a LUX500 4 wire thermostat. I know that the thermostat has a 24v AC supply to it and the digital display is b/u with battery. I am changing to a Lennox G61V hi -eff furnace with 2 stage heating and variable speed DC motor. I was told that I could continue to use my existing t-stat but it would not give me the benefit of a true hi -eff 2 stage heat. Will I have to run new wires if I replace my t-stat or is there one that will give my real 2-stage heat with 4 wires?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 1, 2009, 07:37 AM

    Check the terminal numbers on the lux500. They should be Y R G and W. I could not find a manual. I don't know if the model is power stealing, but in all likyness it doesn't have a common wire (C) which would make it get power rom the furnace. So, you may actually need two more wires: C and (usually W2)

    This thermostat runs with 3 wires. Buy Honeywell VisionPro IAQ Programmable Universal Thermostat with Total Home Comfort Control | Honeywell YTH9421C1002

    Warning: The above is considered a professional thermostat. Help direct from Honeywell will be non-existant.

    By placing an interface box at the furnace.

    There may be other communicating thermostats that can work.

    There are products such as add-a-wire which are difficult to use/install.
    alibaba2's Avatar
    alibaba2 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 1, 2009, 08:23 AM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Check the terminal numbers on the lux500. They should be Y R G and W. I could not find a manual. I don't know if the model is power stealing, but in all likyness it doesn't have a common wire (C) which would make it get power rom the furnace. So, you may actually need two more wires: C and (usually W2)

    This thermostat runs with 3 wires. Buy Honeywell VisionPro IAQ Programmable Universal Thermostat with Total Home Comfort Control | Honeywell YTH9421C1002

    Warning: The above is considered a professional thermostat. Help direct from Honeywell will be non-existant.

    by placing an interface box at the furnace.

    There may be other communicating thermostats that can work.

    There are products such as add-a-wire which are difficult to use/install.
    Thanks for the detailed reply - the Lux 500 has RC RH W Y and G. RC and RH are jumpered out. The 24v supply is taken directly off the power supply inside the furnace through a transformer. I also have 3 more wires which are strung along with the 4 wire sheathed cable but are not connected at either end ( i.e. at the furnace / transformer or the t-stat. ) In your opinion will I still have to run extra wires?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Nov 1, 2009, 09:42 AM

    The new stat will need W2 for the second stage.

    C is generally an optional connection. If C is not used then the thermostat is powered entirely by batteries or through power stealing.

    Between C and (Rc/Rh jumped) you have 24 VAC all the time.

    You have the wires. You can move C and W2 from the furnace to the extra cable and label the ends of the wires.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Nov 1, 2009, 10:37 AM
    OR use this

    Venstar Inc. - Add-A-Wire ACC0410

    Or on some lennox units there are provisions to allow two stage operstion without a two stage thermostat. Read your directions to find out if your unit is one of them that this can be done to.
    OR

    ADD - A - WIRE PART # P474-0410 - eBay (item 160373247349 end time Nov-26-09 11:55:53 PST)

    OR this company makes a real nice setup

    FAST-STAT

    Both of these items have been tested and used at the university in the HVAC lab and they work well. I personally hate to run new thermostat wires from the inside unit to the thermostat or to the outside unit from the insyde unit for a replacement heat pump install.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replacing Old Thermostat with programmable on 2-stage Furnace [ 9 Answers ]

I am trying to replace my old mercury thermostat with a programmable one. The furnace is a realtively newer Carrier: Performance series (Model: 58MTA) 2-stage heat. I have a few probems: 1) There are only 2 wires coming from the wall. I have a feeling that when the previous owner (I'll assume...

2 stage furnace / single stage thermostat [ 1 Answers ]

I am having a Goodman 90,000btu 2 stage, variable speed 5 ton blower furnace put in. I am also have a 3 ton 16 seer A/C put in. They want to set me up with a Honeywell 4000 programmable thermostat. I thought that I read that this thermostat was for single stage heating. Am I getting short changed?...

White rogers thermostat 2 stage heat 1 stage cool [ 6 Answers ]

Anyonw know how to hook this up with a dpdt relay There is 5 wires , outdoor heat for stage 1 heat , propane gas for stage 2 hear Thanks For any help :confused:

White rogers thermostat 2 stage heat 1 stage cool [ 1 Answers ]

What is the right wiring to hook the WHITE ROGERS 80 SERIES thermostat up ( 1F82-261)? I have a outdoor wood burner dlowing hear to a exchanger in the ducts , and I have propand gas as a back up sorce The furnace is a coleman evecon ( 94 model) with ac (up draft) I think I had the wiring...

Honeywell thermostat heat/cool in Rheem 2 stage furnace? [ 1 Answers ]

I have a Honeywell 1 Heat/1Cool thermostat (TH6110D1013) that I would like to use with a Rheem 2 stage gas heat furnace. I think it is possible but would I get the same benefits as having a thermostat with 2 heat/1 cool? Would I just connect the W terminal on the Thermostat to the W2 on the...


View more questions Search