    Spa gfci trips constantly
    I just wired a new spa and the gfci keeps tripping. I know I wired it correctly, It is 6-3 wire with ground The 50 amp gfci subpanel is hot. Every time I try to power up the gfci trips. Any ideas?
    geediddy's Avatar
    geediddy Posts: 11, Reputation: 3
    New Member
     
    #2

    Oct 27, 2009, 12:46 PM

    Kill the power, and take your volt meter and check the continuity between the power legs and ground. Then go to the heater and check for resistance from each of the power legs to ground. You should find your problem. Most of my spa problems have been the heaters they may still work, but they leak voltage to ground and are not safe anymore.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Oct 27, 2009, 12:58 PM

    Possibly not wired right. Probable issues are with line and load neutrals not being kept separate EVERYWHERE. Needs some pics on how the spa panel is wired an how the feed is wired. Use go advanced/manage attachments to post.
    IDman17's Avatar
    IDman17 Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 27, 2009, 01:06 PM

    Problem solved... thanks
    geediddy's Avatar
    geediddy Posts: 11, Reputation: 3
    New Member
     
    #5

    Oct 27, 2009, 09:12 PM

    What was the problem? Don't leave us hanging. Was our advice helpful?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hot tub gfci trips [ 19 Answers ]

I'm about to pull my hair out... Gfci on hot tub trips as soon as breaker in main panel is turned on... replaced breaker with new 50 amp gfi... replaced wires from gfi box to tub... unhooked all plugs on control box... it even trips if you unhook the main hot wires to the tub... with only the...

GFCI trips intermitantly [ 8 Answers ]

The GFCI trips intermitantly on my spa. The Blower was unplugged and the GFCI worked. Another Blower was installed and the GFCI trips again. I say the GFCI works and there is still something wrong in the spa. The Dealer says my GFCI is old and needs better noise suppression. They want to replace it...

3-way switch trips GFCI [ 1 Answers ]

All, I installed a GFCI in a bathroom that has 2 outlets, 2 vanity light bars controlled by a pair of 3-way switches, and a shower room with a Nutone fan/heater/light combo. I installed a GFCI in one outlet and when I turn on the lights, the GFCI trips. Both outlets have two cables in them and...

Submersible pump trips gfci [ 9 Answers ]

My pond pump has been operating for over a year. Recently it tripped the gfci. I pulled it and took it apart but didn't see anything obvious. I pulled the ground wire and tried the pump and it worked. Anyone have any ideas?

Circuit breaker trips constantly [ 2 Answers ]

After eight years in the house without any problems now the oven circuit breaker keeps tripping as soon as the oven is above about 250 C. I turn off everything else that might be on this circuit and still the problem exists. Help!


View more questions Search