    20amp DP Breaker GFCI
    If I install a 20amp DP GFCI breaker will it work correctly if the hot tub works on 240 only.
    The tub has no neutral.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 26, 2009, 01:01 PM

    Yep, but connect the pigtail to line neutral. You can leave load neutral disconnected.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20amp Dp Breaker [ 1 Answers ]

I have a indoor whirl pool need, need 240v 20amp DP breaker to operate. If this tub is hard wired does it need to be on a GFCI?

How to Switch a 20amp breaker to a 30 amp? [ 1 Answers ]

I have friend that works for Oaks Farms. He runs the ice cream to stores and gives them frizer along with the ice cream. Well he actually owns it. He has asked me if I can switch the 20 amp breaker to a 30 amp breaker because the 120 volt receptacle that the freezer is connected to keeps going out...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

15AMP Breaker used instead of 20AMP -ok? [ 4 Answers ]

We just had an electric gate installed that extends across our driveway. I noticed that the installer used a 15 amp breaker switch to connect to for power (the gate is the only device on this breaker). In looking at the manual last night the installation instructions call for a 20 AMP breaker (the...


View more questions Search