New Member
|
|
Jan 9, 2008, 07:20 AM
|
|
15AMP Breaker used instead of 20AMP -ok?
We just had an electric gate installed that extends across our driveway. I noticed that the installer used a 15 amp breaker switch to connect to for power (the gate is the only device on this breaker). In looking at the manual last night the installation instructions call for a 20 AMP breaker (the wording is - "Minimum: 20-amp breaker switch per gate motor needed"). In reviewing this site it looks like the size of the breaker is detemined by the size of the wire used - is this correct? Also, can I assume that if the breaker does not trip I am OK? In other words, I assume a breaker switch that is too small will just constantly trip vs. a breaker that is too large may never trip. Again he was the installation person, not an electrician. Thanks in advance!
|
|
 |
Ultra Member
|
|
Jan 9, 2008, 07:32 AM
|
|
I think you are correct, but I am not an expert, so I want to see what others will say.
|
|
 |
Full Member
|
|
Jan 9, 2008, 07:34 AM
|
|
I'll let the real pros chime in, but if it is 14 gauge wire that he used to install the gate, you don't have a choice, you have to use a 15 amp breaker. If he used 12 gauge, you could use a 20 amp breaker. But you would have to know for sure if the entire run of wire is 12 gauge. On the other hand, if the 15 amp break isn't blowing, then I don't think you have to worry.
|
|
 |
Printers & Electronics Expert
|
|
Jan 9, 2008, 09:40 AM
|
|
No, This the above is not correct>
The size of the conductor is determined from the manufacturer's required amperage.
20 amp demand (Breaker) carries with it requirements for conductors not less than #12 AWG. And a Max 20 amp load.
Two things need to happen very quickly: (1) Contact the electrician and demand his immediate return. He did not follow the installation instructions. Even though he may have sized the load and used the metal information plates to correctley determine the load and conductor size.
(2) [/B] If he installed a 15 amp breaker and connected it to a #12 AWG conductor, only the breaker has to be changed.
However if he installed a 15 amp breaker connected to a #14 AWG conductor, both the breaker and the conductors need to be changed. A 20 amp breaker cannot be connected to any conductor lower than #12 AWG.
|
|
 |
Home Repair & Remodeling Expert
|
|
Jan 9, 2008, 09:43 AM
|
|
Go with Don's explanation. The motor determines the breaker and the breaker determines the wire size. If the installer made the mistake it is his responsiblility to fix it. Just because the breaker doesn't blow is not an OK resaon to leave it.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Switching from 15AMP breaker to 20AMP
[ 6 Answers ]
I am contemplating switching my 15AMP breaker into a 20AMP breaker because the lights flicker in my home office because my computer and printer eat up a lot of power.
If I switch breakers, will this help my power problem? Or I am limited to the gauge of the wires in the wall? Thanks for the...
20amp vs. 15amp outlets
[ 6 Answers ]
Is there anything inherently different between 15amp and 20amp outlets? Outlets labeled 20a are about 3-4 times more expensive than the ones labeled 15a. My buddy with a fair amount of experience advises me to buy 15a outlets and hook them up to my 12 gauge wire running back to 20amp breakers. ...
Adding a 20amp receptacle to a 15amp breaker
[ 2 Answers ]
Hi All,
I need to install a small tankless water heater (made for under the lavatory sink) for the sink in my bathroom. The specs on the water heater are: 120 Volts, 2.4kW, 20 Amps, wire size: 10AWG. My question is this... The existing bathroom outlet that I want to splice into to add this water...
15amp or 20amp?
[ 2 Answers ]
Does the 2005 NEC allow bedroom and living room outlets to be on a 15amp circuit? I am familiar with the 80% rule. Thanks in advance. Tom
Outside GFI circuit - 15amp outlet on 20amp circuit
[ 1 Answers ]
I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...
View more questions
Search
|