    Circulating pump what else could it be
    The heat on the second floor of my home is blowing cold... its a 2 zone weil mclain hydro system... the st floor is hot... the second is cold what I have observed so far

    1. the boiler control unit has a light blinking... limit

    2. if I touch the pipe just below the circulating pump its very hot... just above the pump is warm... as I move away from the boiler a few feet the pipe is cold


    Any ideas?. I took the liberty of putting a new circulating pump just in case... but didn't fix the problem
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 15, 2009, 02:30 PM
    Low system water pressure is the place to look first. You need about 12 pounds for a 2 story.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hot Water Circulating Pump Installation [ 1 Answers ]

Any diagrams or instructions for installation of a closed loop water circulating system with pump?

Should my circulating pump always be running? [ 1 Answers ]

My circulating pump is always running. I have a 3 zone setup and an adjustment dial ranging from 180 to 240 degrees for the circulating pump. It's set to 220. Is that correct and what does it do?

Circulating system [ 5 Answers ]

chuck7071 New Member Join Date: Nov 2007 Posts: 1 I have a 4 or 5 gal. water heater to run 120deg. Water thourgh about 50ft. Of copper line. There is a circulating pump and two relief valves and a one way check valve.The water heater has a relief valve on it also. I want to hook a supply...

How to tell if circulating pump is working [ 2 Answers ]

I have and older Furnace with Hot water Cast Iron radiators (2 floor, 1300 sq ft house). Had to turn on furnace for first time over weekend and it took about 50 min to get the temp from 63 up to 66. The radiators heat unevenly and I was listening for the circulating pump to go on so I could bleed...

How to wire two thermostats to run one circulating pump [ 3 Answers ]

How do you wire two 24v thermostats in two different zones that will run one 110v circulating pump? Thanks


View more questions Search