    #1

    Oct 10, 2009, 11:48 AM
    Furnace won't start
    Hi everyone,
    First time on the site and hope someone can help. I have an armstrong ultra V advantage 93 gas furnace. We turned it on the other day and it would not start up. The diagnostic lights indicate that the pressure switch was in the closed position and wouldn't start. I took the hose off and blew and sucked simultaneously and heard it clicking inside the pressure switch. At this point the induction motor started and the pilot would lite but wouldn't start up. After three tries it stopped trying and the lights indicated that the ignition failed. Can anyone tell me what is going on. I hope that I don't have to call a repairman. Money is tight. Thank you in advance.
    vic559's Avatar
    vic559 Posts: 5, Reputation: 1
    New Member
     
    #2

    Oct 10, 2009, 01:01 PM

    Sound like either your Thermostat not right, did u have an air-con, did that work.
    Or is your thermo couple not working, so the system though you don't need the heat, either way it shoyldn't cost too much
    Hope that help
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #3

    Oct 10, 2009, 01:14 PM

    I don't know that much about Armstrong but some things are the same on all furnaces.

    Please explain one thing, you said the pilot would light, does that mean that a flame would light up or that the ignitor would glow? If you did not have a flame it is possible the gas valve is turned off, if you did have a flame on the pilot then never mind my answer. But if you will give us more info about how your furnace is suppose to work we may can help.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Oct 10, 2009, 02:10 PM

    How many pressure swithces are on your furnace? Im guessing you saw the glow plug(orange glow) instead of a pilot. If you have two pressure switches, one will allow glow plug to burn, and other will allow gas valve to open. When you pulled the hose off the pressure switch, did you notice any water? If so, you may have plugged drain hoses, which will cause both pressure switches to act up.

    Now, turn power off to furnace,, wait a few seconds, turn it back on and tell us exactly what happens... It should go like this,, thermostat calls for heat, draft inducer comes on for a predetermined amount of time(lets just say 15 to 30 seconds), then glow plug or spark ignition starts, then main burners lite, then after a predetermined amount of time(say between 30 seconds and a minute ) the blower comes on. Of course this is all assuming you don't have a pilot. Hope we can help. Lee.
    ironicone91's Avatar
    ironicone91 Posts: 4, Reputation: 1
    New Member
     
    #5

    Oct 10, 2009, 02:36 PM
    Quote Originally Posted by mygirlsdad77 View Post
    how many pressure swithces are on your furnace? Im guessing you saw the glow plug(orange glow) instead of a pilot. If you have two pressure switches, one will allow glow plug to burn, and other will allow gas valve to open. When you pulled the hose off of the pressure switch, did you notice any water? If so, you may have plugged drain hoses, which will cause both pressure switches to act up.

    Now, turn power off to furnace,,, wait a few seconds, turn it back on and tell us exactly what happens....It should go like this,,,,thermostat calls for heat, draft inducer comes on for a predetermined amount of time(lets just say 15 to 30 seconds), then glow plug or spark ignition starts, then main burners lite, then after a predetermined amount of time(say between 30 seconds and a minute ) the blower comes on. Of course this is all assuming you dont have a pilot. Hope we can help. Lee.
    Yes the glow plug was glowing then I heard a click from the gas valve and flames ignited and shot into the furnace but when the glow plug stopped glowing the fire quit and nothing lit up in the furnace.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Oct 10, 2009, 02:52 PM

    Sounds like your flame senser is dirty. The flame senser does exactly what it is called,, it senses the flame,, if burners lite, then go out once glow plug shuts down, then the flame senser is not sensing the flame and will shut off gas to burners. Flame senser is located on burner assembly, it will have one wire going to it,, only one, and is usually mounted with one screw.. the flame senser will either be straight, or L shaped,, it has a porcelin body where it mounts to burner assembly, and a metal rod that sits directly in the flame. Take it out, clean it with steel wool, sand cloth, fine sand paper , or any abbrasive material,, till it shines like new. Put it back in and let me know how it works. I've posted a pic of an average flame senser, but there are many different makes. Lee.
    Attached Images
     
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #7

    Oct 10, 2009, 02:59 PM

    WOW VIC,that post confused me a little! Anyway,I agree, sounds like a dirty flame sensor,Armstrong uses a inermitent pilot, pilot lights,senses flame and then lights the main burners. Be really careful when removing the pilot assembly, the ignitor breaks really easy.
    ironicone91's Avatar
    ironicone91 Posts: 4, Reputation: 1
    New Member
     
    #8

    Oct 10, 2009, 04:06 PM
    Quote Originally Posted by mygirlsdad77 View Post
    sounds like your flame senser is dirty. the flame senser does exactly what it is called,,,it senses the flame,,, if burners lite, then go out once glow plug shuts down, then the flame senser is not sensing the flame and will shut off gas to burners. flame senser is located on burner assembly, it will have one wire going to it,,,only one, and is usually mounted with one screw.. the flame senser will either be straight, or L shaped,,, it has a porcelin body where it mounts to burner assembly, and a metal rod that sits directly in the flame. Take it out, clean it with steel wool, sand cloth, fine sand paper , or any abbrasive material,,,till it shines like new. Put it back in and let me know how it works. ive posted a pic of an average flame senser, but there are many different makes. Lee.
    I took the sensor out and sanded it but it still does same thing
    vic559's Avatar
    vic559 Posts: 5, Reputation: 1
    New Member
     
    #9

    Oct 11, 2009, 08:24 AM

    Hi hvacservicetech_07
    Basically that's what I trying to say like everyone else
    The sensor most likely cost trouble, and is happening to older unit once or twice in their life time, when thing get to use for a long time, just like a wear and tare thing, I say change it will solve the problem,
    But stronger advice do not try to do it yourself, unless you really for sure what are you doing, is a safety concern.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #10

    Oct 11, 2009, 11:28 AM

    vic, you said you thought it was the thermocouple,, this unit does not have a thermoscouple, it has a flame senser, which rarely needs to be replaced, usually only needs cleaning,,

    Iron, can you post a pic of the flame senser you cleaned? I just need to clear this up for my own purposes,, really curious as to what your flame senser looks like. Lee.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #11

    Oct 11, 2009, 01:25 PM

    I agree, a piture would be helpful. I'm about 90% sure that Armstrong uses an intermittent pilot, older used a sparker and the newer stuff runs hot surface. I'm curious as well.
    ironicone91's Avatar
    ironicone91 Posts: 4, Reputation: 1
    New Member
     
    #12

    Oct 11, 2009, 04:50 PM
    Quote Originally Posted by mygirlsdad77 View Post
    vic, you said you thought it was the thermocouple,,,this unit does not have a thermoscouple,, it has a flame senser, which rarely needs to be replaced, usually only needs cleaning,,,

    Iron, can you post a pic of the flame senser you cleaned? I just need to clear this up for my own purposes,,,really curious as to what your flame senser looks like. Lee.
    I can't post a pic but it is basically about a two inch metal rod about an eighth of an inch in diameter with about a half of an inch of ceramic at the top. It is right beside the glow plug and sticks down right in front of one of the burners. It has one screw holding it down. And one wire going to it on top.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #13

    Oct 12, 2009, 03:12 PM

    Okay, you cleaned the right thing. As I said before, normally cleaning the flame senser does the trick, but I have seen them go bad.. So I suggest installing a new flame senser and see what happens. I have also seen bad flame senser wires, and also, it could be your control board has a problem. I would start with the flame senser itself, but your best bet would be to have an hvac tech in to trouble shoot the system, I understand times are tight, but they would be able to find and fix your problem in short order. Please let us know how you make out. Lee.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

1997 honda civic dx won't crank won't start [ 17 Answers ]

I have a 1997 honda civic dx 5 speed. Yesterday car was fine, started strong and drove strong. I parked car last night and about 4-5 hours later tried to start it. When I turned the key in the ignition there was no crank at all. I can hear a little hum and then a click but that's all.

Saturn won't start, power locks won't work, radio resets itself. [ 4 Answers ]

My 99 Saturn has had some starting problems in the past. It would sometimes not start but if you let it sit from anywhere from 45 minutes to 24 hours, it would eventually start. Or, after having Dad look at it, we could tap the starter and it would work. So we thought it was the starter. I...

My furnace won't light and the lights on my control module won't come on [ 2 Answers ]

Ok a couple of question if you can help I have a comfortmaker furnace I believe 1999 it came on a couple of times after I bought a new transformer, board, capacitator, and ignition control module now it won't come back on What to Do! Also I wanted to know if you can tell me the difference between...

Kenmore he4 panel won't work and dryer won't start [ 1 Answers ]

I have had the circuit board/panel replaced once on my he4. I had only 2 weeks left on the warranty and figured it should be OK once it was fixed. They wanted another $200 to renew the warranty! Didn't have the $$ at the time. Anyway, the same darn thing is happening... you have to push the buttons...