Can I tap into an existing outlet that has more than three wires
I want to install an additional outlet under the counter in my bathroom. There is only one other outlet in the room and there are multiple wires wire nutted together in the box, but only three connected to the duplex. Can I connect to the vacant poles on the duplex and run the cable to my new outlet or will that be too many wires in the box.
|
|
 |
Ultra Member
|
|
Sep 30, 2009, 06:57 PM
|
|
The way you described connecting the nuw pug is right if you are sure to connect the ground wire also.
As far as too many wires I an not sure that you don't already have two many wires in that box. Maybe an expert will give you the right answer.
You might take out the box that the old plug is in and put back in an extended box, I think that would alow extra wires.
|
|
 |
Uber Member
|
|
Oct 1, 2009, 02:41 AM
|
|
Need to know:
1. What size box, height, width, and depth, and shape.
2. How many total wires.
3.What size wires.
|
|
 |
New Member
|
|
Oct 1, 2009, 10:43 AM
|
|
The box is 3.5"x3.5"x2" and has two Romex 12ga. Cable in it now.
|
|
 |
New Member
|
|
Oct 1, 2009, 02:20 PM
|
|
 Originally Posted by tkrussell
Need to know:
1. What size box, height, width, and depth, and shape.
2. How many total wires.
3.What size wires.
The box is 3.5" x 2" x 3.5 and has two 12 gauge Romex cables coming into the box. They are all wire nutted together (black to black, white to white and ground to ground) with leads coming from the wire nuts to the existing GFCI outlet.
|
|
 |
Full Member
|
|
Oct 3, 2009, 07:37 PM
|
|
That's a 24.5 cu. in. box
Each 12AWG wire needs 2.25 cu. in. so there is enough room for 10 in that box.
Your current box fill count is 7
4-12AWG current carrying conductors originating from outside the box.
1- all equipment grounds
2- the duplex receptacle
All that is longhand for yes you can add another piece of 12-2 w/g romex to the box and extend your circuit to a new receptacle.
I wish more people knew enough to ask this type of question.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Outlet box with too many wires
[ 2 Answers ]
Outlet box with fan, outlet, light combo, replaced switch and the outlet,
Now the light will work but no power to the outlet, and the fan, Since I have
Replaced the outlet,switch combo I cannot power up the outlet,
Now the problem is frustrating me because when the existing wiring that...
230 volt welder with 2 wires outlet with 3 wires.
[ 7 Answers ]
Hello. I have an older stick welder that has a ground, white wire and black wire. The outlet I have to connect to has a ground, black, white and red wire. Is there a way I can connect the old welder to the newer wires? I know the red and black are hot but what about the common white wire? What...
Moving existing outlet 3"
[ 6 Answers ]
I just did a bathroom remodel and the vanity is higher than the old one. In order for it to be above the backsplash it needs to go up about 3". Can and how do I move it?
GFI-6 wires to one outlet
[ 1 Answers ]
My question is that I have an outlet in the bathroom right next to the sink. (Big NO NO) This outlet has 3 whites to it and 3 blacks to it with the proper grounds. This would place it in the middle of a series. How do I distinguish the line and the loads to replace the outlet with a GFI Outlet??...
Adding wires to existing box.
[ 4 Answers ]
I recently asked a question about adding a ceiling fan where there wasn't previously a fixture and got my question answered. So, I now know what my plan is for wiring it together.
My next question might be a stupid one, but I just thought of it and without experimenting or asking, I don't know...
View more questions
Search
|