    Main breaker circuit
    Today my whole house main breaker circuit tripped. I went and reset it. After 5 minutes it tripped again. I have my pool equipment and a/c running. I decided to reset it but this time I turn off the a/c breaker. Everything is working fine until I turn the a/c breaker backed on. It tripped again after 5 minutes. I then reset the main breaker. This time I turn off the pool pump and run one of the a/c. No trip from the main breaker. Could my main breaker went bad. BTW it's a 150 Square D.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 27, 2009, 05:48 AM
    More than likely it is a bad connection somewhere at or near the breaker. This is NOT something you should mess with yourself. An electrician would need to have the power company cut the power to replace the breaker if that is what is needed.

    Call someone ASAP!
    thi7b's Avatar
    thi7b Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 27, 2009, 07:59 AM
    Can I shut off the main breaker to check for bad connection.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Sep 27, 2009, 08:12 AM

    The short answer is no, because the main breaker is always powered.

    The long answer is yes, but it involves measuring the voltage between the cable (not terminal) of where the main power coes in and the panel bus with a sensitive voltmeter capable of measuring in millivolts when under load. This isn't recommended for the novice)

    Measuring the temperature of the breaker housing is another way. A finger can work, so can an IR thermometer.

    The loose connection can be anywhere. The main panel, breaker, the meter, or the overhead connection.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can my Circuit breakers add up to more than my main breaker? [ 6 Answers ]

I have a 100 amp main and all of the circuit breakers in my main service panel and my sub-panel add up to about 180 amps. Is this all right or do I need to upgrade to a 200 amp main? Any help would be appreciated thanks!

Override Main Circuit Breaker [ 4 Answers ]

I am planning of installing two instant water heaters each rated at 240V/60A My electricity company will not provide MCB higher than 50A Does anyone know of any solution to override the MCB? Use of AC capacitors (e.g. charging at 20A to 720V and discharging at 60A at 240V) If such solution is...

Main circuit breaker missing a handle tie. [ 1 Answers ]

I have a Culter Hammer circuit breaker panel with (2) 100 amp main breakers that are not tied together. A home inspector said they should be tied. Is he correct? If so can I add a tie or do I have to replace the breakers?

Main circuit breaker [ 12 Answers ]

The main circuit breaker keeps triping when it gets hot could it be old and need changing

Blowing Main Circuit Breaker [ 1 Answers ]

I have a electric dryer that is 220 volt. When I turn it on, after about 15 minutes it doesn't blow it's own 30 amp breaker, but blows the 100 amp main breaker. I can shut off the 30 amp breaker specifically for the dryer and it shuts it off. Any ideas??


View more questions Search