    Replaced wall sockets, breaker over loaded
    Hi, I replaced the wall sockets on the main floor (13 of them). I installed the wires exactly the same. Origionally the kitchen was on 2 breakers, however now when I try to switch one breaker "on" it pops right away, and the other does nothing. I was told by the people at reno that I need to remove the tab on the sockets that have a "red" wire. I have 3 sockets with red wires. I ckecked the old plugs and 4 of them have the tab removed. I did not pay attention to this when I did replacement. I donot know whick plugs need to have the tab removed to allow the kitchen plugs to be separated onto the two breakers. Can anyone help? Thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Sep 5, 2009, 06:04 AM

    The red and black can share 1 neutral, could be as easy as breaking off tabs where they have a red and black.
    You could remove the reds, turn both breakers on and look for 240 volts between the black on receptacle and red wire, if 240 volts, tab should be broke.
    mattvit's Avatar
    mattvit Posts: 73, Reputation: 1
    Junior Member
     
    #3

    Sep 5, 2009, 07:02 AM

    Problem is fixed. I missed 1 red wire socket. Removed the tab and everything is fine

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Replaced circuit breaker still no power to garage [ 5 Answers ]

There was an overload many times on this specific breaker, and we replaced it and there is still no power to the garage. It was a double switch 20 amp circuit breaker/fuse that was replaced, and the main switch outside to the power was shut off before we replaced the breaker. There was a severe...

Current in Ground wire in wall sockets [ 8 Answers ]

I live in delhi india and around 2 years back moved into an apartment where I got the rewiring done. It seemed OK until the aircon switch in the voltage stabiliser kept burning up and had a foul odour. So I read up on it and checked polarities and it was reversed. But in the wall socket...

I have replaced the bad circuit breaker. But no electricity. [ 1 Answers ]

Hello, I had an old and broken circuit breaker that I have recently replaced it to a new one. But, my electric outlets and lights are still not working. Its not getting any juice, period. All the other ones are working fine just the one that I have replaced is not... please, help:confused:

Can 15 amp breaker be replaced with 20 amp? [ 4 Answers ]

I want to plug in a refrigerator in a garage space which is on a 15 amp circuit. Can the breaker switch be replaced with a 20 amp breaker to support the extra load?

Light sockets keep resetting breaker [ 5 Answers ]

Hi All, I have a bathroom socket that periodically trips the breaker when a portable heater is used. One of my outside covered sockets is on the same line and occasionally tripped the breaker when we had the pool pump plugged in. Sometimes all I needed to do was press the reset button on the...


View more questions Search