    50 Amp Double Oven Connected to #8 Gauge Wire
    The installation instructions for this double oven read:

    "This oven requires a separate, grounded 4-wire, 240V (AC), 50 Amp service with its own circuit breaker. Installation must comply with National Electric Code... We strongly recommed connecting this oven to No. 8 gauge copper wire."

    Here is the question: Doesn't a 50 Amp circuit require #6 gauge wire? Why are they recommending #8 gauge wire when, according to my knowledge, #8 is only used for 40 Amps or less?

    Any clarification would be greatly appreciated! Thanks in advanced!
    alargent's Avatar
    alargent Posts: 2, Reputation: 1
    New Member
     
    #2

    Sep 23, 2010, 09:53 PM
    According to the NEC, a #8 wire can handle 50 Amps but only if that wire is THHN (or equivalent) and is pulled as single wires (75 degrees C). If you are using Romex (NM cable) which most houses have, then you must use the 60 degree C column which shows 40 amps maximum on #8 wire and so you would have to use a 40-Amp breaker to protect the #8 wire. A double oven wall unit does not receive any exceptions from NEC 220.55 so you must use the nameplate rating or the manufacturer's instructions. Using 6/3 Romex (NM Cable) with a 50-amp, double-pole breaker is the best way to go.
    alargent's Avatar
    alargent Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 23, 2010, 09:53 PM
    According to the NEC, a #8 wire can handle 50 Amps but only if that wire is THHN (or equivalent) and is pulled as single wires (75 degrees C). If you are using Romex (NM cable) which most houses have, then you must use the 60 degree C column which shows 40 amps maximum on #8 wire and so you would have to use a 40-Amp breaker to protect the #8 wire. A double oven wall unit does not receive any exceptions from NEC 220.55 so you must use the nameplate rating or the manufacturer's instructions. Using 6/3 Romex (NM Cable) with a 50-amp, double-pole breaker is the best way to go.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

5o Amp Double Oven Connected to #8 Gauge Wire [ 1 Answers ]

The installation instructions for this double oven read: "This oven requires a separate, grounded 4-wire, 240V (AC), 50 Amp service with its own circuit breaker. Installation must comply with National Electric Code... We strongly recommed connecting this oven to No. 8 gauge copper wire." ...

Connecting 12 gauge and 14 gauge wire [ 4 Answers ]

Is it ever acceptable to attach 14 gauge to 12 gauge wire? I have a remodel situation where I have a 20 amp/12 gauge wired circuit powering outlets only. I want to tap off the end-of-run outlet to power an electric-venting skylight. The skylight comes with 14/2 wire. Can I tap off the 20 amp...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

Wire gauge for Double oven hook up [ 7 Answers ]

I am replacing old oven with double oven, current oven is on a 20 amp breaker, old wiring can not make out the gauge. The new double oven is convection 27" ovens, the following is the Power Specs: Amp Rating at 240V 30 Bake Wattage 2640 Broiler Wattage 3400 Convection Wattage 2500 KW...


View more questions Search