    5o Amp Double Oven Connected to #8 Gauge Wire
    The installation instructions for this double oven read:

    "This oven requires a separate, grounded 4-wire, 240V (AC), 50 Amp service with its own circuit breaker. Installation must comply with National Electric Code... We strongly recommed connecting this oven to No. 8 gauge copper wire."

    Here is the question: Doesn't a 50 Amp circuit require #6 gauge wire? Why are they recommending #8 gauge wire when, according to my knowledge, #8 is only used for 40 Amps or less?

    Any clarification would be greatly appreciated! Thanks in advanced!
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Sep 2, 2009, 03:25 PM

    You are partially correct. It depends on the type of insulation and it's temperature rating. #8 Romex and UF cable is limited to 40 amps. USE and THWN are rated for 50 amps, THHW is rated for 55 amps. USE is often used for stove circuits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

Is it safe to replacing a lighter gauge wire with a heavier gauge [ 11 Answers ]

Hi all, One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?

Connecting 12 gauge and 14 gauge wire [ 4 Answers ]

Is it ever acceptable to attach 14 gauge to 12 gauge wire? I have a remodel situation where I have a 20 amp/12 gauge wired circuit powering outlets only. I want to tap off the end-of-run outlet to power an electric-venting skylight. The skylight comes with 14/2 wire. Can I tap off the 20 amp...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

Wire gauge for Double oven hook up [ 7 Answers ]

I am replacing old oven with double oven, current oven is on a 20 amp breaker, old wiring can not make out the gauge. The new double oven is convection 27" ovens, the following is the Power Specs: Amp Rating at 240V 30 Bake Wattage 2640 Broiler Wattage 3400 Convection Wattage 2500 KW...


View more questions Search