    Capacity of old panelboard
    Hello,

    I am checking to see if the panelboard in the old building can handle my load
    (considering a restaurant in this building)

    The old square-D panelboard label reads:

    Power <<<< >>>> lights
    ------------------------------------
    90 << bus amp>> 175
    120-240 << bus volts >> 120-240
    3-ph 4 w <<phase>> 1-ph 3 wire
    60 <<cycles>> 60

    There is also a B-stinger service for an old (unused) elevator

    Question: how much current I can draw from this panel?
    My equiment requires 200A 110V

    Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 24, 2006, 04:21 AM
    So do you have a 90 amp 120/208 volt 3 phase panel and a 175 amp 120/240 volt single phase panel?

    That's what I get from:
    90 << bus amp>> 175
    120-240 << bus volts >> 120-240
    3-ph 4 w <<phase>> 1-ph 3 wire


    Not sure what a B-stinger service is.

    How did you arrive at your equipment needs 200 amp 110volt? Did you add the load for each appliance to arrive at a total of 200 amp?


    Are you sure you do not have any 208 volt 3 phase or 240 volt 1 phase restaurant equipment? I have done many restaurants and even the smallest one has something 208-240 volts.

    Can you help with more detail and answer my questions and we can go from there.

    Generally speaking, the load is added to arrive at a total connected load, and increase that by 25% to arrive at the panel or service size.

    Thanks
    bbhatt's Avatar
    bbhatt Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 24, 2006, 08:09 AM
    Quote Originally Posted by tkrussell
    So do you have a 90 amp 120/208 volt 3 phase panel and a 175 amp 120/240 volt single phase panel?
    Hello, here are some more details,

    Not sure what a B-stinger service is.

    Reply>> B-stinger is a center tapped delta secondary of the transformer that reads 240 to ground, other two phases read 110 to ground (also known as dog-leg) - found in older buildings.

    How did you arrive at your equipment needs 200 amp 110volt? Did you add the load for each appliance to arrive at a total of 200 amp?

    Reply>> I added everything + 25% of total + 25% of largest load


    Are you sure you do not have any 208 volt 3 phase or 240 volt 1 phase restaurant equipment? I have done many restaurants and even the smallest one has something 208-240 volts.

    Reply>> correct, I do not have anything that needs 208/240V, the stinger leg (240v) was used for on an old elevator that since has been taken out of service

    I would like to know what total current I can reasonably get out of this panel, one electrician said I don't need a new panel, other said I do, the city inspector said "you might",

    Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 24, 2006, 09:00 AM
    Ok, wow have not run into this for a long while, we call it the "bastard" leg. I suppose b-stinger is more socially acceptable.

    So is the delta panel the 175 amp? Or the 90? I am still a bit confused about which panel is which.

    Obviously, as you probably know,you cannot use the B phase on the delta panel for any 120 volt circuits.

    FYI, the center leg should colored orange.

    Derate each leg or phase of each panel by 80%, and that is what is allowed for load. If this helps, great, if not get back with more questions.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Light switch capacity [ 8 Answers ]

I recently installed 5 recessed lighting fixtures on the same circuit and all these lights turned off at one time after a few minutes. They did not trip the circuit breaker. I then turned the light switch off for a few minutes and then the lights could be turned on for a few minutes. The light...

Mean capacity [ 1 Answers ]

A particular type of plastic soap bottle is designed to have a capacity of 15 ounces. There is a variation in the bottle manufacturing process. Based on historical data, suppose that the bottle capacity can be reasonably modeled by a normal distribution with a mean of 15 ounces and a standard...

Hard drive Capacity [ 3 Answers ]

?? I have Microsoft Windows XP operating system. I have a 40GB hard drive that shows only about 7GB capacity. How do I fix this problem without losing my data. I don't have a zip drive to backup everything. Please Help!?

Hard drive Capacity [ 2 Answers ]

?? I have Microsoft Windows XP operating system. I have a 40GB hard drive that shows only about 7GB capacity. How do I fix this problem without losing my data. I don't have a zip drive to backup everything. Please Help!


View more questions Search