  • Oct 23, 2006, 10:14 PM
    bbhatt
    Capacity of old panelboard
    Hello,

    I am checking to see if the panelboard in the old building can handle my load
    (considering a restaurant in this building)

    The old square-D panelboard label reads:

    Power <<<< >>>> lights
    ------------------------------------
    90 << bus amp>> 175
    120-240 << bus volts >> 120-240
    3-ph 4 w <<phase>> 1-ph 3 wire
    60 <<cycles>> 60

    There is also a B-stinger service for an old (unused) elevator

    Question: how much current I can draw from this panel?
    My equiment requires 200A 110V

    Thank you
  • Oct 24, 2006, 04:21 AM
    tkrussell
    So do you have a 90 amp 120/208 volt 3 phase panel and a 175 amp 120/240 volt single phase panel?

    That's what I get from:
    90 << bus amp>> 175
    120-240 << bus volts >> 120-240
    3-ph 4 w <<phase>> 1-ph 3 wire


    Not sure what a B-stinger service is.

    How did you arrive at your equipment needs 200 amp 110volt? Did you add the load for each appliance to arrive at a total of 200 amp?


    Are you sure you do not have any 208 volt 3 phase or 240 volt 1 phase restaurant equipment? I have done many restaurants and even the smallest one has something 208-240 volts.

    Can you help with more detail and answer my questions and we can go from there.

    Generally speaking, the load is added to arrive at a total connected load, and increase that by 25% to arrive at the panel or service size.

    Thanks
  • Oct 24, 2006, 08:09 AM
    bbhatt
    Quote:

    Originally Posted by tkrussell
    So do you have a 90 amp 120/208 volt 3 phase panel and a 175 amp 120/240 volt single phase panel?

    Hello, here are some more details,

    Not sure what a B-stinger service is.

    Reply>> B-stinger is a center tapped delta secondary of the transformer that reads 240 to ground, other two phases read 110 to ground (also known as dog-leg) - found in older buildings.

    How did you arrive at your equipment needs 200 amp 110volt? Did you add the load for each appliance to arrive at a total of 200 amp?

    Reply>> I added everything + 25% of total + 25% of largest load


    Are you sure you do not have any 208 volt 3 phase or 240 volt 1 phase restaurant equipment? I have done many restaurants and even the smallest one has something 208-240 volts.

    Reply>> correct, I do not have anything that needs 208/240V, the stinger leg (240v) was used for on an old elevator that since has been taken out of service

    I would like to know what total current I can reasonably get out of this panel, one electrician said I don't need a new panel, other said I do, the city inspector said "you might",

    Thank you
  • Oct 24, 2006, 09:00 AM
    tkrussell
    Ok, wow have not run into this for a long while, we call it the "bastard" leg. I suppose b-stinger is more socially acceptable.

    So is the delta panel the 175 amp? Or the 90? I am still a bit confused about which panel is which.

    Obviously, as you probably know,you cannot use the B phase on the delta panel for any 120 volt circuits.

    FYI, the center leg should colored orange.

    Derate each leg or phase of each panel by 80%, and that is what is allowed for load. If this helps, great, if not get back with more questions.