    Install new t-stat, fan and heat work but compressor will not turn on?
    Hello all. I replaced our old turn dial thermostat with a programmable digital thermostat (Honeywell thx6400b). I turned off the breakers for the house prior to opening up the old thermostat, where I found a green, yellow, red and white wire attached. I removed the old t-stat and hooked up the wires to their corresponding spots on the new one (which includes an Rc and Rh input with a wire jumper between the two... ). However, when I turned on the power, only the fan and heat settings work - the air being blown out is not being cooled. It worked perfectly before my tstat swap.

    I checked the compressor and it is no longer running. None of the circuit breakers in the breaker box are tripped, and the fuse on the actual furnace/control board unit in our basement is fine. The problem persisted even when I reinstalled the old tstat, so I assume I must have done something to the compressor itself. When I short the red and yellow wires together, the compressor will make a clicking noise, but does not start up even after waiting for hours (I understand that most units have a delay)... instead, the blower simply pushes luke warm air out the registers. I have opened up the compressor unit's back panel, but do not see any fuses or breakers to check. There is a power switch next to the compressor (mounted on the outside wall), but no outside breaker next to it At this point, I have simply disconnected the tstat wires and am letting the unit sit idle, hoping that it might simply have an overload shutdown that was tripped and needs to sit for an hour or two before resetting. In the meanwhile, any ideas what might be wrong or what I should try next?

    Not sure if this changes the diagnosis, but the compressor is a Lennox 10ACB48-11P. I do not havea meter reader to determine whether the various connections are at the correct voltage.

    Thanks in advance for your thoughts.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Aug 11, 2009, 07:16 PM
    Sounds like you need to re-look at your wiring
    Like the wire that goes to the ac
    With the jumper that sends power to ac if wires are in right spot
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Aug 11, 2009, 11:07 PM

    To clarify "what does turning off the house breakers" mean?

    Turned off all of them? The main?
    Just the air handler?
    The condensing unit and the air handler?

    The R to Y click caused a click to be heard in the outside unit. Yes? No?

    If your comfortable doing this, it's worth a try. Using the outside disconnect, disconnect the outside unit. Usually it's a pull out with an on and off position. You basically pull, rotate and insert it back again. The on position usually has a higher insertion force.

    So, pull the disconnect.

    Take off the cover of the condenser and trace the two small tstat wires and the power wires. They should terminate at a relay (contactor) and it probably has exposed contacts.

    You can leave the disconnect off for the next test. When there is a call for cool the contacts should touch and it should click.

    I bet it does. Does it?

    If yes, (assuming nothing changed) then the likely cause is no 240 VAC. You can turn the tstat to off and put the disconnect back in, in the ON position and test, but I'll bet you get the same result. Click, but unit won't turn on.

    Now if, you didn't turn off power to the outside unit (A high amperage connected breaker) when you replaced the tstat, then you may have a broken breaker. Try to reset it and try again.

    When you don't wait for 2 minutes when engaging the compressor, large surges can develop and take out the breaker.

    Your going to need a meter or a test light to troubleshoot further plus the skills not to get shocked.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox heat turn off and turn back on to work [ 2 Answers ]

I have a lennox heater I have to turn it off and turn it back on to get it to heat. What is wrong and how do I fix it.

Heat blower does not turn - Air Handler does not turn on for heat [ 7 Answers ]

I have an Energy Kinetics System 2000 boiler. It is hooked up to two different zones (two different air handlers). Zone 1 (main house) when turned on at the thermostat clicks and calls for heat, the boiler starts for a bit but the fan/blower never kicks on. Zone 2 (master bedroom) works just...

New stat now no work [ 1 Answers ]

Have a heat only furnace reran new wirex3 red white green hooked up to new stat now will not turn on at all furnace or fan that is trying to heat house with wood burner and just run fan

Blower will not turn on on cooling but will work on heat? [ 6 Answers ]

My central a/c system inside blower will not turn on during cooling it will turn on during heat. Everything else on the system works. My system is over 13 years old.

Replaced T-stat batteries... Now the AC/HEAT does not work at all! [ 5 Answers ]

Good morning and Happy Columbus Day everyone. I must say that anyone's help and feedback will be much appreciated. Last night the Thermostat (Honeywell Programmable CT8602) gave the low battery light as my wife was looking to drop it a degree before bed so she decided to replace the batteries. ...


View more questions Search