    Compatible compressor and evap coil
    Working on a goodman outdoor unit ,model#crt18-1
    I have an air handler not sure what brand model#FFIDNE024(think it is a janitrol)

    Are the evap coil and condensing unit compatible?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 10, 2009, 09:43 PM
    From the numbers it looks like you have a 18,000 outdoor unit and a 24,000 indoor unit. Since the inside has a larger capacity than the outdoor the units will work together BUT You will have to use the metering device/piston for the outdoor unit size since the outdoor unit size controls the system size so to speak. Actually you would be better off using a expansion valve but that is another story.

    A good contractor will be able to set the correct system charge after all the appropriate refrigeration steps are taken for the professional install.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Evap coil only half cold [ 3 Answers ]

My evaporator coil will only get ice cold on the lower portion and the upper half is warm . What would cause this problem, possible restriction?

Mismatched compressor and coil [ 1 Answers ]

I have a 5 yr old heat pump. The compressor is a 12 seer. When it was installed they also installed a new coil but it turns out that it was a 10 seer coil. The system has worked perfectly for 5 years. The technician who tuned up the system today (and discovered the mismatch) said I should...

Airmax evap coil & sp6 start capacitor [ 1 Answers ]

Anybody ever hear of airmax and have spec info on the coils? Would a model # AC48/22+NBEXV4 mean it's a 4 ton coil per the 48 in the model number? Would having an old 4 ton coil mismatched to a new 2.5 ton SEER 13 condenser cause lack of cooling on warm days? Also what does a sp6 "start...

Replace 2-year evap. Coil because of sulphur? [ 3 Answers ]

System is two years old. Wouldn't cool so I set up a service appointment, thinking it was low on freon. 2 hours and $160 later, repair guy says I have a bad evap coil, caused from sulphur in my well water that emits fumes and deteriorated my coil. Talked to a couple of hvac people and they say...

New Evap Coil for Carrier - refrigerant and price [ 1 Answers ]

I have a 12-year-old Carrier Heat pump. The AC repairman, who was in fixing the control board which had been knocked out by a lightning strike, mentioned that the coil had a lot of rust on it and would soon start developing small leaks. He also mentioned that the refrigerant it used would be phased...


View more questions Search