    I have goodman variable speed air handler and a 14 seer 410a unit, along with a Honeywell programmable 2 stage thermostat. The fan ramps up and down continuously when the temperature is near the set point. I've had it looked at a couple times now and nothing. Does anyone have any suggestions or adjustments that can be done to get this air handler working right?
    Shouldn't the air handler run in a low speed when it close to the set point and high when under a high load?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Aug 9, 2009, 08:49 PM

    Post model numbers of both, especially of tstat. A link to the tsat manual would be ideal for starters.

    Also describe where your thermostat is located such as hall, inside wall, outside wall, proximity to windows, direct sun and registers.
    Schultzt's Avatar
    Schultzt Posts: 4, Reputation: 1
    New Member
     
    #3

    Aug 10, 2009, 06:29 AM
    Thanks for the reply and no problem. The info is below:

    The air handler is the Goodman AEPF1830 which is the 1.5-2.5 ton R410A unit. It's located in the basement and only used for AC, we have water baseboard heat. The compressor is the Goodman 2 ton SSX14024. After looking at wiring diagrams on the Alpine site, my system also has Y1 also hooked up to the air handler and thermostat, they show it not attached for AC only systems. Should this be disconnected?
    Air handler manuals: http://www.alpinehomeair.com/viewpro...ions_brochures
    Compressor manuals: http://www.alpinehomeair.com/viewpro...ions_brochures

    The thermostat is the Honeywell vision pro TH8320U1008. It's located on the inside hall wall. Direct sun is not able to shine on it. The ac vents are blowing away from it and into other rooms. There are no AC vents in the hall where it's located.
    The full manual can be located here: http://www.pexsupply.com/Honeywell-T...Cool-3911000-p.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Aug 10, 2009, 12:40 PM

    Make a note of the previous values of the tstat parameters:

    Verify that 0170, system type is 1; Cool only

    Use the system test mode and check the cooling and fan as well as stage 2 and report back.

    If it's two speed, you should probably be using Rc, Y and Y2; C is optional.

    What's the value of param 0530 adaptive recovery?
    Schultzt's Avatar
    Schultzt Posts: 4, Reputation: 1
    New Member
     
    #5

    Aug 10, 2009, 08:51 PM

    OK the thermostat was setup wrong. It was set to 2 stage but my compressor is only a single stage. I set 170 to "1". I thought I had a 2 stage but after looking though the systems, I would have had to buy the 16 seer system with the two stage compressor
    .
    The system check worked.

    The adaptive was set to "on", I turned it off but no luck.

    I even disconnected the Y2 but the system still ramps up and down while the AC is running
    .
    Any other suggestions?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Aug 10, 2009, 09:56 PM
    Make sure that the following is set to off

    0530 is off

    0650 is off

    0660 is off

    It seems the thermostat is butting heads with the air handler controls

    Post back with results
    Schultzt's Avatar
    Schultzt Posts: 4, Reputation: 1
    New Member
     
    #7

    Aug 11, 2009, 06:05 AM

    Yes all of those are off. I noticed during the ramping up and down the thermostat isn't clicking any relays on and off so now I'm suspecting that it's with the air handler.

    I'll go through the wiring diagrams for air handler tonight, maybe the installer miswired something there? I'm also going to pull the filter as make sure that's not clogged.

    I would also like to decrease the CFM a little, because it's louder than I would like and it cools plenty fast on a 90 degree day. If I were to do this do I risk freezing up the coil?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Aug 11, 2009, 07:05 AM
    Actually the speeds should be set using a meter for that purpose. If the blower speed is not adjusted correctly it can cause problems. Usually a quality installer will adjust the fan speeds for both heat and cool after the install is complete to assure proper operation. The new style furnaces are not user friendly when it comes to adjustments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need for speed 2 special edition , not running at all [ 6 Answers ]

Prob in playing NFS 2 SE Well there is a huge problem I am facing these days , long long ago I played this lovely game , now when I again wanted to play the same , I downloaded this game 4 times from net and none of the games worked , 3 games are around 90 mb and one is around 450mb , now when I...

21 hp briggs OHV engine not running at max speed [ 1 Answers ]

The hard plastic gear on the bottom of the flywheel complete broke off,the starter gear looks fine.I bought a new flywheel gear and installed it.After I got every thing put back together and started the lawnmower up,I noticed when you run at full throttle it is not running at full speed.When you...

Lawn tractor starts, ramps up, then almost turns off, then ramps up, and on and on [ 1 Answers ]

I have a sears lawn tractor, has worked fine most of the time, but now it is cycling through something: I was mowing, and suddenly lost power, and it almost turned off, but then it ramped up to full throttle, and kept this cycle up. I checked the fuel, plenty available. Checked oil, fine. I...

Ruud varible speed air handler [ 3 Answers ]

I am installing a new two stage heat pump, rudd IUHPL. The 24 volt transformer is in the air handler. The transformer is energized and putting out 24 vt. Which enters the circuit board. The red wire leaving the board is 0 vt. As I understand the system this red wire is supposed to supply 24 vt to...

Running speed [ 2 Answers ]

How to sprint faster


View more questions Search