    whou69's Avatar
    whou69 Posts: 13, Reputation: 1
    New Member
     
    #1

    Aug 9, 2009, 07:56 AM
    A/C failed to turn on, how to re-connect control wires ?
    I have this split body A/C, that I haven't been able to turn on this season, when I noticed the thermostat does not draw any voltage, after days of troubleshooting I noticed that the previous owner disconnected this wire from condenser, (they used window a/c to save money).

    Now I have to connect this wire back to control circuit in the condenser. This 24 vac line has two wires: yellow and red, and control wire come out of condenser has blue,pink,and white, how shall shall I connect them ?

    I have enclose the contactor picture as follow, thanks for your attention. The power line come up in the middle, control line goes down to the right bottom leads to air handler. That disconnected 24 vac line is not shown.

    http://im1.shutterfly.com/media/47b9...D550/ry%3D400/
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Aug 9, 2009, 08:30 AM

    If it is bttween the blue, pink and white, I would disconnect the blue, pink, and white
    Then set thermostat to cool, you should look for 24 volts AC on 2 of the 3 wires. Remember or write down the 2 colors, turn unit off and connect to the wires going to the Contactor coil(brown and purple)
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Aug 9, 2009, 08:32 AM
    Also check that copper is not exposed where the purple and blue wires connect at wirenut.
    whou69's Avatar
    whou69 Posts: 13, Reputation: 1
    New Member
     
    #4

    Aug 9, 2009, 09:24 AM
    Quote Originally Posted by Stratmando View Post
    If it is bttween the blue, pink and white, I would disconnect the blue, pink, and white
    then set thermostat to cool, you should look for 24 volts AC on 2 of the 3 wires. Remember or write down the 2 colors, turn unit off and connect to the wires going to the Contactor coil(brown and purple)
    Thanks for the reply, but the voltage bearing control wire is not yet connected, there won't be any voltage across any of the control lines. I can trace the white and pink lines go to the thermostat, and blue line goes to the relay next to air handler motor.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Aug 9, 2009, 10:47 AM

    You need 2 conductors to contactor coil, 1 from thermostat, and the other side of transformer is gotten from thermostat or air handler, you will see 24 volts between the correct 2.
    whou69's Avatar
    whou69 Posts: 13, Reputation: 1
    New Member
     
    #6

    Aug 9, 2009, 07:11 PM
    Thanks will try this
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Aug 9, 2009, 09:17 PM

    I see blue and white connected in the condenser and red(pink) taped off. This is fine.

    One of these wires goes to Y of the tstat. Doesn't matter which.

    The other goes to common (C) on the transformer. This could be tricky to find.
    whou69's Avatar
    whou69 Posts: 13, Reputation: 1
    New Member
     
    #8

    Aug 11, 2009, 05:13 AM

    Thanks for the reply.

    Both pink and white wire connected to the tstat, actually the white wire goes to the Y terminal on tstat, the blue wire goes to one side of blower relay;

    Yellow and red transformed line (not shown in the picture) were not labeled at transformer, how can I test which is common ? And how do I connected these two wires back to the condenser in the picture ?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #9

    Aug 11, 2009, 05:28 AM

    You are using blue and white at compressor and pink and white at thermostat. Need to use 1 pair only.
    I usually see the compressor control wires go to Air Handler, also Thermostat wiring between thermostat and Air Handler.
    Whad do you have between T-stat and air handler? I would hook blue from thermostat to compressor contactor coil. With out any testing you can hook other wire to either transformer wire 50/50 chance, it will work or it won't, then it is other wire.
    A meter will show 24 volts between blue and white when set to cool.
    whou69's Avatar
    whou69 Posts: 13, Reputation: 1
    New Member
     
    #10

    Aug 11, 2009, 09:20 AM
    HTML Code:
    <pre>
    
                   [relay for a/h]      [contactor coil]
                          o     o             o    o
    [tstat]               |     |             |    |
                          |     |    blue     |    |
    blue  o---------------+     +-------------o    |         o-------- yellow
                                     white         |           24 vac  to be connected
    white o----------------------------------------o         o-------- red
                                     pink
    pink  o--------------------------------------------o
    
    
    
    
    Here's basic schematic for control wires, as you can see, b/w tstat and air handler
    there's only one relay.
    </pre>
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Aug 11, 2009, 09:27 AM

    I usually see a red wire (24 volts from transformer) to thermostat Red, then when you select cool, the red connects to green for the blower fan relay, and blue for cool(compressor contactor)
    The white from thermostat to air handler is usually for heat.
    Blue usually doesn't go to relay then contactor unless it has a circuit board.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Four way switch wires won't connect [ 3 Answers ]

Hi I have a four way switch in place so that there are 3 switches in our hall to work the one bulb. I replaced all switches with a chrome finish and everything was great until I forgot to label the wires on the four way, now I have the four way with four wires but I have no idea where they all go....

How do I connect wires from Janitrol to the Honeywell Thermostat [ 1 Answers ]

How do I connect the wires from a Janitrol to the Honeywell RTH7500 Thermostat. I have the following wires: R Red Y Yellow G Green O Orange W2 White E Beige/Pink C Blue Black wire not connected

How to connect wires to a RTH6300B honeywell thermostat [ 2 Answers ]

I only have 2 wires to connect I removed the old wires from the W and R connection And put them on the new one but nothing happens. Any help would be appreciated

Hampton Bay Thermostatic Remote Control Failed [ 2 Answers ]