    What size wire do I use for a new 200amp service 550ft away?
    I want to run a new 200amp service wire to a shed 550ft from my meter. I have checked with the electrical company and the meter is sufficient to run this with my house, there is also an extra set of lugs. Also do I need to run this in condut. What would be better copper or aluminum.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 9, 2009, 04:42 AM
    Doesn't anyone ever have a shed or workshop close to home anymore?

    A shed with a 200 amp service? Must be one hell of a shed.

    550 feet is a long distance to deliver 120 volts, even 240.

    The most important variable needed to calculate voltage drop is the running amp load.

    Another aspect is motor load. While a motor may draw say 20 amps running, it will draw up to 60 amps briefly to start under load. A motor starting will affect the voltage drop and possibly prevent the motor from starting properly, if the wire is not large enough.

    That being said, if I assume that a 200 amp would be loaded to the max allowed load on a 200 amp feeder, 80% or 160 amps, at 240 volts, wire size would need to be 1000 MCM aluminum.

    If I assumed 50 amps at 120 volts, which could be more closer to a real scenario, then 500 MCM aluminum would be needed.


    So what will be the amp load, and types of loads in this shed?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size for a 400 amp service [ 2 Answers ]

Anyone know the minimum wire size and conduit I can use for a 400 amp service for my apt building?:confused:

What size wire to use for new service? [ 2 Answers ]

We are currently building a greenhouse, and I need to run about 240 foot of wire from the pole to the greenhouse breaker box. The greenhouse will have 2- 115/230V fans drawing 6.0 amps each, 3- 1/3hp sump pumps not sure of the amperage yet but will be 115v, LP gas instant hot water heater, 10...

Wire Size For 200 Amp Service [ 2 Answers ]

Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run. Lost in paradis... :) :confused:

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search