    Evaporator coil - central air
    I was given a newer Carrier central air unit ("N" coil and Condenser, etc.). The problem is that I have a Lennox furnace and the "N" coil is slightly smaller than the plenum opening above the furnace. If the "N" coil was installed there would be a lot of air bypassing the coil.
    Do I need to get a specific sized coil to match the make of the furnace?
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jul 26, 2009, 02:22 PM
    I`ve worked on some units in the past and I found this to have happened before. What they did was to use sheet metal and filled in the sides of the furnace that wasn`t covered by the evap.coil and by doing that all the forced air had no choice but to go through the coil and not around it. It seemed to be working pretty well with no complaints from the home owner
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Jul 26, 2009, 02:29 PM
    Put a access door on that carrier N coil. They have been known to have leak problems unless they have fixed that problem by now.
    richard truex's Avatar
    richard truex Posts: 7, Reputation: 1
    New Member
     
    #4

    Jul 27, 2009, 06:53 AM
    Quote Originally Posted by hvac1000 View Post
    Put a access door on that carrier N coil. They have been known to have leak problems unless they have fixed that problem by now.

    My concern is "choking down" the furnace plenum by sheet metaling to get all the air through the coil.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jul 27, 2009, 07:34 AM
    Some newer style coils are smaller than the original and some are larger. If the coil has a size tag and it is a 2 ton coil it will do 2 tons of cooling etc. You have provided no pictures so it is difficult to tell exactly how bad this chocking problem might be ot if you need to install turn/vanes ora tapered system to have smooth air flow. Take some pictures and post them. We will have a look see.
    richard truex's Avatar
    richard truex Posts: 7, Reputation: 1
    New Member
     
    #6

    Jul 27, 2009, 11:09 AM
    Quote Originally Posted by hvac1000 View Post
    Some newer style coils are smaller than the original and some are larger. If the coil has a size tag and it is a 2 ton coil it will do 2 tons of cooling etc. You have provided no pictures so it is difficult to tell exactly how bad this chocking problem might be ot if you need to install turn/vanes ora tapered system to have smooth air flow. Take some pictures and post them. we will have a look see.
    Thanks I will do asap...
    richard truex's Avatar
    richard truex Posts: 7, Reputation: 1
    New Member
     
    #7

    Jul 29, 2009, 06:31 AM
    Quote Originally Posted by hvac1000 View Post
    Some newer style coils are smaller than the original and some are larger. If the coil has a size tag and it is a 2 ton coil it will do 2 tons of cooling etc. You have provided no pictures so it is difficult to tell exactly how bad this chocking problem might be ot if you need to install turn/vanes ora tapered system to have smooth air flow. Take some pictures and post them. we will have a look see.
    Photo attached (I hope) of furnace insides.

    Here are dimensions:

    Furnace plenum:
    Depth 20"
    Width 21.25"

    Coil:
    Depth 18"
    Width 14.5"

    Thanks!
    Attached Images
  1. File Type: pdf Photo 2.pdf (775.9 KB, 315 views)
  2. hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #8

    Jul 29, 2009, 09:37 AM
    You will have to pan in the area so the new coil has something to sit on. The coil cabinet/plenum seems to already have a access door so that is a good thing.

    Now if it were me I would build or have built a taper seat or perch for that new coil. This will elevate the coil some but would make for smoother air transfer across it. This would also help eliminate any choking of the air flow.

    One other item to consider is to use a larger coil for a 3 ton system. I have no idea what that size would be but it might have a larger base. If you went that route you would just use the same size flow rater/piston/or expansion valve as the 2 ton coil would use. It will give a larger wet surface area and would also help with moisture removal.

    You are not a pro at this so you might seek some advise from where you bought the equipment since there are options to be considered and a perch or panning to do so the coil will fit properly.

    I am not there and I do not do drawings/design work here so all I can do is give you good advice and ideas.
    richard truex's Avatar
    richard truex Posts: 7, Reputation: 1
    New Member
     
    #9

    Jul 29, 2009, 04:56 PM
    Quote Originally Posted by hvac1000 View Post
    You will have to pan in the area so the new coil has something to sit on. The coil cabinet/plenum seems to already have a access door so that is a good thing.

    Now if it were me I would build or have built a taper seat or perch for that new coil. This will elevate the coil some but would make for smoother air transfer across it. This would also help eliminate any choking of the air flow.

    One other item to consider is to use a larger coil for a 3 ton system. I have no idea what that size would be but it might have a larger base. If you went that route you would just use the same size flow rater/piston/or expansion valve as the 2 ton coil would use. It will give a larger wet surface area and would also help with moisture removal.

    You are not a pro at this so you might seek some advise from where you bought the equipment since there are options to be considered and a perch or panning to do so the coil will fit properly.

    I am not there and I do not do drawings/design work here so all I can do is give you good advice and ideas.

    Thank you!

    If I understand correctly it would be a tapered perch forcing all air through the coil - correct?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #10

    Jul 29, 2009, 05:14 PM
    Yes that is what I call it but I am an old man. I am sure there are different names for it but a old sheetmetal guy will understand.
    richard truex's Avatar
    richard truex Posts: 7, Reputation: 1
    New Member
     
    #11

    Jul 30, 2009, 02:09 PM
    Quote Originally Posted by hvac1000 View Post
    Yes that is what I call it but I am an old man. I am sure there are different names for it but a old sheetmetal guy will understand.
    Thanks for your help!

    Can I use regular plumbing silver solder for the copper supply lines?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #12

    Jul 30, 2009, 07:55 PM
    Only Braze the copper lines. I am not cheap so I use 15% stick but other % will work. Also you should have a little nitrogen flow while brazing and protect all valves etc with Zorba the Heat or wet rag to prevent any damage.

    See some links here

    Proper brazing copper lines - Google Search=

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Central air evaporator coil [ 2 Answers ]

Where is the evaporator in central air and how do I clean it.not low on feon just had it put in thought that was problem,but ran OK for a while and then fan stayed on in outside unit and iced HELP!! God Bless

Cleaning My Evaporator Coil [ 6 Answers ]

I need to clean my evaporator coil on my Central HVAC (heat pump) unit. I have used a softbristle brush on my sweeper and there are still fuzzy stuff left up there. I am don't want to damage or bend my coils so what do you suggest I can use to get the rest off? Would Scrubbing Bubbles work OK or...

A/C Evaporator coil placement [ 2 Answers ]

Is it more efficient to have the air condition evaporator coil place in the attic of the 2nd floor of a two story home or have the evap. Coil place in the attic above the first floor and then run the duct up to the 2nd floor and down the 1st floor? I was told that it is more efficient for the evap...