-   -   Using Double pole circuit breaker for two separate circuits (https://www.askmehelpdesk.com/showthread.php?t=370595)

  • Jun 30, 2009, 11:14 AM
    hthierry
    Using Double pole circuit breaker for two separate circuits
    I am wiring my basement with 3 circuits for about 24 receptacles. We used to have electric baseboard heat and the 20 Amp Double pole breakers from the heaters are still there but disconnected. Can I use each double pole breaker for two separate circuits? Can I use one leg of another double pole breaker for a circuit? Am I being dangerous as well as a cheapskate?
  • Jun 30, 2009, 11:22 AM
    crigby

    Hi,
    Yes you can use both sides of the unused breaker each for different circuits, and the 20 Amp rating calls for 12 AWG wire to be correct.
    I am unsure about the other; do you mean to say it is unused? If so then I would say yes. If not I would consider another alternative. One might be to change a single breaker to a double, if you have no room to add another breaker.
    The important consideration is that the totals for all circuits used do not exceed the rated amperage of your box/service.
    Peace,
    Clarke
  • Jun 30, 2009, 11:37 AM
    tkrussell

    A typical single pole circuit breaker, new, only costs about $4-$6 each.

    If you need three, that would be the most $18.00.

    Splurge and buy new circuit breakers.