Wiring from old ruum tstat to hunter tstat
First pic is my old tstat - I believe it is a heat pump.
(note that orange wire and gray wires are not used, E and W2 are jumped)
Second pic is the new tstat's wiring explanation. Hunter Model 44860.
So I wired the wires as such:
Old->New
G->G
R->Rc/R
B->B
Y->Y1
W2->W2, jumped with E
X->C
O and L are not used on both new and old.
Y2 is now used on the new tstat.
Now, I turn it on and no matter what mode it is (heat/cool/auto) it seems like only the heater is turned on. What did I do wrong?
|
|
 |
New Member
|
|
Jun 20, 2009, 11:09 AM
|
|
Sorry, here are the pics...
|
|
 |
Ultra Member
|
|
Jun 20, 2009, 11:16 AM
|
|
Check the installation instructions for any reference to an "R"-"Rc" jumper. Disconnect and insulate the black wire and the orange wire. They were previously unused and should remain that way. If possible, post a better pic of the new wire connections (they are a little cut off in the current pic).
|
|
 |
New Member
|
|
Jun 20, 2009, 11:19 AM
|
|
 Originally Posted by KC13
Check the installation instructions for any reference to an "R"-"Rc" jumper.
R/Rc is 1 connector, there is also RH connector, but I'm sure it isn't used for heat pump system.
BTW, RH connector is not connected now;
|
|
 |
Ultra Member
|
|
Jun 20, 2009, 11:21 AM
|
|
 Originally Posted by rbleader
R/Rc is 1 connector, there is also RH connector, but I'm sure it isn't used for heat pump system.
Betcha it is...
|
|
 |
New Member
|
|
Jun 20, 2009, 11:24 AM
|
|
 Originally Posted by KC13
Betcha it is...
Jumped Rc/R with RH, still heater only.
|
|
 |
Ultra Member
|
|
Jun 20, 2009, 11:43 AM
|
|
 Originally Posted by KC13
If possible, post a better pic of the new wire connections (they are a little cut off in the current pic).
This would be very helpful.
|
|
 |
New Member
|
|
Jun 20, 2009, 12:02 PM
|
|
 Originally Posted by KC13
This would be very helpful.
Here it is, it's a mess, but...
Old->New
G->G
R->Rc/R (currently jumped with RH)
B->B
Y->Y1
W2->W2, jumped with E
X->C
O, L, Y2 are empty.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Honeywell to Hunter tstat
[ 6 Answers ]
I am wanting to replace my old Honeywell Chromotherm III to a Hunter Set & Save 44260.
The wiring from the old is: W-white, G-green, C-blue, R-red, Y-yellow and orange is not connected (O,W,G,C,R,Rc,B,Y).
My new one is labeled G,RC,RH,Y/O,W/B & Y1 with RC & RH jumped.
I have gone through most of...
Switching from Rudd tstat to hunter tstat
[ 1 Answers ]
I have a single stage heatpump. I changed the tstat out yesterday to a new hunter manual tstat, worked fine last night. Came home from work today and it was very hot in the house,only the fan was running. Now the outdoor unit will not come on at all. I am wondering if there was a mix up when wiring...
TSTAT wiring
[ 2 Answers ]
I am replacing a Robertshaw 9520 TSTAT with a Carrier TSTATCCREC01. The current wiring on 9520 goes to these terminals. W2 has only a jumper.
R,
Y1,
O,
G,
E,
C,
And a jumper from W2 to E.
The carrier terminals are as follows:
Tstat wiring
[ 4 Answers ]
I am putting in a honeywell tstat TH8110U, and have two wires coming out the wall (white and black). Is the white the heat relay?
Heating & AC Wiring from Handler to TSTAT
[ 8 Answers ]
Hi,
I just bought this house and did not realize that the Central Air/Heat wiring were all disconnected. The handyman want it $500 to wire this. I see no point of spending this type of money just for connect these wire.
I hope someone here can help me on these connections. I don't know much...
View more questions
Search
|