    TSTAT wiring
    I am replacing a Robertshaw 9520 TSTAT with a Carrier TSTATCCREC01. The current wiring on 9520 goes to these terminals. W2 has only a jumper.
    R,
    Y1,
    O,
    G,
    E,
    C,
    And a jumper from W2 to E.

    The carrier terminals are as follows:
    C,
    G,
    Y1,
    O,
    W1,
    R,
    Y2,
    W2.

    They show the following wiring for a six wire, 1 stage cooling, and 2 stage heating heatpump:
    Old wiring designation first:
    R to R,
    Y1 to Y1,
    O to O,
    G to G,
    W2 to W2,
    C to C.
    I am confused since 9520 currently has no wire to the W2 except the jumper from E. Would I hook up according to these directions and hook the old E black wire to W2, and not install a jumper? Help is appreciated! Bruce
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Dec 2, 2005, 10:41 AM
    Neither anybody else here or I seem to have the info you need. You may have to do some more digging yourself. Whoever sold you the thermostat should be willing to answer a few questions too. Did it come with much in directions? Does your system expect the thermostat to choose a heating rate? Are the E and W2 for different heating rates? Unless either your heating unit or the new thermostat are set up to choose different heating rates, I would jumper both heating rates to the terminal on the thermostat that signals for heat. Also, where is the control for the supplementary heat, air handler, thermostat, or manual?

    The new thermostat has all the same terminals as the old except for W1 and Y2. My guess is that the Y2 is for a second A/C rate, and you should leave it unconnected. It sounds like W1 replaces E for one heating rate. Unless the new thermostat gives directions for controlling the heating rate, I would jumper W1 and W2, and connect the wire that went to E to one of them. Even if the thermostat and heating system are both set up to have the thermostat select different heating rates, you would need a 7'th wire for the thermostat to control it.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Dec 7, 2005, 05:24 PM
    I didn't find your email until today. Looking at the single stage cooling 2 stage heat pump, if that is what you have, I assume you already have it all connected up if your system has the terminals listed. If you still need help, let me know. Posting here is better than email. Not only will I find it faster, but others drop in sometimes with good ideas.

    My Yahoo account fills up with spam and messages from All Experts, and sometimes I don't find things until I work at cleaning out my inbox.

    Those were useful links you posted. I can use them to be more helpful in areas where I have less experience.

    http://www.icca.invensys.com/manuals...w/110-733c.pdf

    http://www.thermostatusa.com/pdf/CCR...stallation.pdf
    G or F Fan G
    Y1, Y or C Cooling Y1
    W1,O,B
    W1, W or H Heating
    Rh, R, M, Vr, A Power R
    C Common C*
    W1,O,B**
    O/B Rev. Valve
    2nd Stage Cool
    Y2 Y2
    2nd Stage Heat
    W2 W2
    RS+5 Remote Sensor +5vdc
    RS Remote Sensor Signal
    RS G Remote Sensor Ground
    CK1 Dry Contact Switch
    CK2 Dry Contact
    * C may not be used on all systems.
    ** O/B is used if your system is a Heat Pump.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Programmable tstat on baseboard heat [ 3 Answers ]

I bought a low voltage thermostat to work with my electric baseboard heat. It is a low voltage system with two transformers that I can see in my crawlspace. Is low voltage the same as millivolt or do I need to make sure which I have and which the tstat works with? I've got two wires coming to...

Wiring help [ 1 Answers ]

We are trying to hang a ceiling fan in our bedroom. We ran into some problems and had to put in a new electrical box causing us to cut some wires. We now have no way to connect these wires back up to complete connection. The wires are older and are the thick copper wires making the use of a wire...

Tstat wiring - dual transformer, 1 "R" connection [ 1 Answers ]

I have a dual transformer system - one for heat, one for cool. The Thermostat I'm replacing has an Rc and an Rh connection. The new Thermostat has a single R connection. The transformers are in phase With each other, however, the heat one puts out 24vac, while the Cooling one is at 26.7vac. Can...

Tstat wiring [ 4 Answers ]

I am putting in a honeywell tstat TH8110U, and have two wires coming out the wall (white and black). Is the white the heat relay?

Heating & AC Wiring from Handler to TSTAT [ 8 Answers ]

Hi, I just bought this house and did not realize that the Central Air/Heat wiring were all disconnected. The handyman want it $500 to wire this. I see no point of spending this type of money just for connect these wire. I hope someone here can help me on these connections. I don't know much...


View more questions Search