    No status light on furnace control board
    I have a goodman
    Board number 1012-930 or B18099-05
    The status light is off and the machine will not do anything.
    I have 24 AC going to the board when the door switch is made.

    Is there a print of the board or does the status light off mean its dead?
    monsterbuck's Avatar
    monsterbuck Posts: 4, Reputation: 1
    New Member
     
    #2

    Jun 16, 2009, 06:11 PM

    Is there a fuse? Just had a problem similar to that today and when I replaced the fuse and had the door switch made, the status light lights up. Mine was a 3 amp fuse.
    arcadiomir's Avatar
    arcadiomir Posts: 1, Reputation: 1
    New Member
     
    #3

    Jan 17, 2011, 06:29 PM
    Monster Buck is right you should measure across the Fuse with your volt meter it should read 0Volts AC if it reads 24 your fuse is Bad, if the fuse is good then the next is the rectifiers at wich point you might be better off replacing the board.
    jakej's Avatar
    jakej Posts: 2, Reputation: 1
    New Member
     
    #4

    Feb 8, 2011, 12:34 AM
    I had a similar problem. My status light went off and hpf wouldn't work so I switched it to lpf and it works juss fine but it doesn't hit as hard. What's the problem? I checked every wire and fuse in my whole system and everythin is juss fine except my status light and hpf doesn't want to work.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier/Bryant Furnace control board . [ 9 Answers ]

I replaced Carrier/Bryant board and the led is flashing rapidly.. what can be wrong? It looked like there's problem with polarity,but everything is fine, the led is still flashing.. uff.. Led Code: Continuous on rapid flashing-Line voltage 115 polarity reversed.If twinned,refer to twinnig kit...

Bad Furnace Control Board? [ 6 Answers ]

I have a Carrier 58PAV that intermittently aborts or sometimes clicks on and off at the draft blower stage. I found out I can move the control board (HK42FZ007) when the blower motor clicks off, and it clicks and comes right back on. If I hold it just right, the furnace starts and if I manage to...

Testing control board on heil furnace [ 5 Answers ]

I have 110 volts going into smart valve but no voltage comeing out to blower motor. Could a bad control board cause this or is it the smart valve ?

Furnace control board fuse keeps blowing [ 1 Answers ]

Hi, I have a Carrier furnace 48GS-036090311TP with a Honeywell T8401C thermostat. I can run the fan on continuously but when I put the Heat to ON on the T-stat, the 5 Amp fuse on the control board (LH33WP003A) in the furnace blows. The sequence is like this: 1. Fan only operation is running...

Powering the G terminal on my furnace control board [ 1 Answers ]

Hi! My furnace's control board recently blew and the repair guy replaced it with a different kind. Aparently the new board requires a wire from the thermostat to the G terminal to work the A/C fan, and the old one didn't. The repair guy would need to make another trip for this repair. I am...


View more questions Search