Sharing a nipple with 2 feeds?
OK, quick setup: I have a meter housing that feeds out to an outdoor panel mounted to the side of the house. This panel has feed through lugs which feed a 40/40 panel in the house (mounted back to back with the outdoor panel using a 2 1/2 inch by 4 inch long nipple.)
This is a new installation
What I am looking to do is to run wires back through the same nipple, into the outdoor panel and out to the shed to run the well pump. So I have the 3/0 wire running through there already to feed the inside panel, but is it acceptable to run wires back through there from a breaker in the inside panel and then exit the outdoor panel through my conduit?
If it is not allowable, can you give me the NEC article that covers this? (I am under 2005 if it matters.)
The reason I want to do this this versus just putting the breaker in the outdoor panel is that eventually I am going to put an auto-transfer switch between the outdoor panel and the indoor panel. I would like the well to work while on generator power.
(Let me know if I left out any important info.) And thank you in advance.
|
|
 |
Senior Member
|
|
Jun 16, 2009, 12:19 AM
|
|
Yes, if the conductors from the meter to the subpanel are feeders. No if they are service entrance conductors. See 230.7
|
|
 |
-
|
|
Jun 16, 2009, 08:09 AM
|
|
That is exactly the type of answer I was looking for. (I hate when people spew info and don't back it up. I am not here just for an answer, rather I wanted a little education too.)
To clarify this is the way I now understand it to be.
Meter Can >>> Outdoor Panel >>> Indoor Panel
>>> = nipple or conduit
No additional conductors may share the nipple between the Meter Can and Outdoor Panel (because of those conductors being non-over current protected.) However, the second nipple, between the Outdoor Panel and Indoor Panel, can contain multiple circuits.
Hope this is correct.
Thank you so much for your reply and the article number. :)
|
|
 |
Senior Member
|
|
Jun 16, 2009, 08:43 AM
|
|
No additional conductors may share the nipple between the Meter Can and Outdoor Panel (because of those conductors being non-over current protected.) However, the second nipple, between the Outdoor Panel and Indoor Panel, can contain multiple circuits.
Hope this is correct.
Yes, if the main is located in the meter.
|
|
 |
Senior Member
|
|
Jun 16, 2009, 08:47 AM
|
|
To be honest, the rule is stupid (230.7)--seeing that we share branch circuit conductors with Service entrance conductors all the time!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Why have overnight feeds resumed?
[ 4 Answers ]
My 17 week old baby boy has started waking up several times overnight for feeds. He was a great sleeper and was going all night until about 2 weeks ago when he strated waking up at 12 midnight and then 4ish and then 7 ish again! Why is he doing this? Any advice anyone? Its my second baby and...
Power feeds for two switches?
[ 4 Answers ]
I am wiring my basement and I have two dimmer switches in one double receptical, do I need two power feeds to power the lights or is their away to do it with one? I am using 14/2 wire.
Satellite Feeds
[ 2 Answers ]
Sorry, didn't see a better section for this...
I run a small community news website/cable TV show and we sometimes come across the need to receive satellite feeds. The local school has a dish and so does a local TV station, but that's extremely inconvenient.
I'm looking into receiving KU...
Night feeds?
[ 8 Answers ]
My daughter is 2 years and a few months old.
She never took to the bottle so I was breast feeding her up until 2 years.She did drink milk during the times she was awake,but she used to cry a lot in her sleep if I did not feed her.
We could not make her stop breast feeding.
Now she has...
Installation of Automatic Feeds
[ 1 Answers ]
Hey Guys, sorry I haven't been in contact for so long, truth is that I've been away and yes happy to return. That said, lets get straight down to business. I would like some advice on the installation of an automatic feed to my basement boiler system, actually, my six boilers. I currently have...
View more questions
Search
|