    Capacitor for new motor
    I just had to buy a new condenser motor for my unit. The NEW motor says that it needs a - 3 MFD +- 5%, 370 VAC Run Capacitor. The OLD motor was setup with a 45/5 MFD +-6%, 370 VAC Dual Capacitor which had a wire from the compressor and the fan wires. Do I just need to run a jumper to the 3 MFD form the old 5MFD Com terminal to make this work, or is there that big of a difference with the capacitors that I don’t need to use the 3MFD?
    BTW… I need to replace the old 5MFD capacitor anyway so is there maybe another capacitor I should go with instead?
    Thanks in advance for you help.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jun 15, 2009, 05:44 PM
    Leave the original dual capacitor where it is and alone,take off only the wires that go to the old motor
    The new motot need the 3 MFD +-5% only
    You probably have 2 brown wires, one solid--one brown /with white stripe
    Land those 2 wires only (one on each side of the new capacitor
    The other wires are to go to where the load is connected,probably to the contacter
    Make sure the new motor is running in the correct direction,and the fan blade is on right

    Hope this is simple enough and is a help to you
    User73's Avatar
    User73 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 15, 2009, 07:10 PM

    I should have noted that the new motor (like the old one) only has three wires - Black and the Orange going to the LINE, and then the Brown going to the capacitor then on to the Orange. This is what makes me think that the new capacitor (3MFD) needs the jumper from the old 5MDF capacitor to the terminal connected to the Orange on the new.

    E.g. – the original wiring was Black – to the contactor, Brown – to the FAN terminal on the capacitor, Orange to the COM terminal which also had a Red wire coming form the contactor, and a Yellow from the compressor to the HERM terminal capacitor.

    So now I'm thinking - Yellow stays put in to 5MFD cap, Red stays put…continue Red on from old cap terminal to new 3MFD cap terminal next to the Orange and Brown on the other new terminal. Black still to contactor.
    Does that sound right?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Capacitor or motor [ 9 Answers ]

How do I know whether my capacitor or blower motor is at fault. My blower motor is weak and won't blow the a/c to the 2nd floor. This is a new problem for a 20 year old unit. Thanks Al

AC Fan Motor, capacitor, or what? [ 9 Answers ]

I had the fan motor of my outdoor AC unit replaced about 5 years ago, it has an AO Smith mod F48K92A01 which I found online for about $65 but want to make sure it is not possibly the capacitor or something else first. I caught the unit having the fan hitting the splicer near the top, clank,...

Capacitor for toy motor [ 3 Answers ]

hey ^-^ hmm recently I've taken apart one of my old toy cars from way back when. The main reason being that I wanted to make a sort of hand crank flashlight using the motor. The motor originally took five double A batteries, so I assumed, perhaps incorrectly, that it would be able to put out about...

Motor or Capacitor? [ 2 Answers ]

How can you rule out a bad capacitor? Is the only way by ohms?


View more questions Search