    200 amp panel
    I have a 200 amp 30 space main breaker homeline panel. I want to remove the 200 amp breaker and make it a 100 amp panel. I shouldn't have any issues with what, should I?
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Jun 13, 2009, 06:37 PM

    Why are you doing this.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jun 13, 2009, 06:44 PM
    I concur with Chuck. Why would you need to do this?

    It can be done with a 100A back-feed breaker but you need to install a breaker hold down.
    kich1031's Avatar
    kich1031 Posts: 26, Reputation: 3
    New Member
     
    #4

    Jun 13, 2009, 06:48 PM

    I can't find a 100 amp 30 space panel anywhere. I don't have a supply house close by and the 100 amp panel that I need to replace is only a 20 space.

    Basically, I need more space and I don't want to have to do a heavy-up
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #5

    Jun 13, 2009, 07:01 PM

    So basically you have 100 amp service to the building. And you are just wanting to use the box itself and change out the main to use it for 100 amp
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #6

    Jun 13, 2009, 07:42 PM

    What are you adding that you need more spaces?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jun 13, 2009, 07:52 PM
    Just install a sub-panel or replace the existing with a 30 space 100A panel.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jun 14, 2009, 04:12 AM
    The issue is once you remove the 200 amp breaker from the 200 amp panel, you violate the UL listing of that panel. Therefore your plan is not allowed.

    So I concur with Stan, get the proper panel.

    Jerro brings up a good point, what do you need to add? The concern is are you sure the existing 100 amp service can handle the added load.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

Interior 4 panel doors separating at panel joint [ 1 Answers ]

I had my entire interior house repainted last fall. All the doors, which are wood 4 panel very good quality are all separating where the sunken panel meets the wood around the door. Not sure I am explaining this correctly but I hope someone gets the picture... The doors have been in this house...

Wiring from my house panel to my pole barn panel [ 1 Answers ]

I am going to be wiring my pole barn up soon and just need some help on the type of wire to use. In my house I have a 200 AMP service and plan on running a 100 AMP feeder from that panel to my subpanel in the barn. (Just under 100 Feet) I am going to run a 6 gauge ground, two 4 gauge...

Max Amps in a Panel and adding a sub panel for more circuits [ 3 Answers ]

Hello all, I recently moved into a condo with a 200 amp panel (in my unit). The main panel is in the electrical room of the building and my unit was previously a commercial retail space. I did some remodeling and my panel is now full. The total combined amps of all the circuit breakers...

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...


View more questions Search