    Air freezing up
    I have a Janitrol ac system in my home. We have noticed that it is freezing up inside our basement and the lines are backed up with water and are leaking. We just had the compressor replaced about a month ago and freeon was put in.. What could be causing this to happen and is there something that we can do to keep from calling a costly repair man.. Thanks
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Jun 13, 2009, 04:40 AM
    Possibilities... 1) Inadequate indoor airflow. Dirty/clogged air filter and/or indoor coil, blocked supply and/or return air ducts, blower not operating correctly. 2) Inadequate refrigerant charge, usually due to leakage. System pressures/temperatures are lower than intended design, causing airborn water vapor to freeze on indoor coil surface (rather than just collecting and draining away). 3) Underloaded system. Operating the air conditioner when indoor and/or outdoor temperatures are relatively low.
    la29freeman's Avatar
    la29freeman Posts: 4, Reputation: 1
    New Member
     
    #3

    Jun 13, 2009, 06:52 AM

    Thanks for the reply KC13. Is there anyway that we can check the freeon to see if it is leaking or is low. We have checked the coils are they are clean and have changed the filter.. still no change
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Jun 13, 2009, 02:07 PM

    Was the filter very dirty? Did you give the unit time to unthaw??
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Jun 14, 2009, 06:03 AM
    If you just had the compressor replaced, the entire system should have been evacuated (pumped into a vacuum) with a micron gauge to assure against leaks. Look for oily residue where the new work was performed. If present, try applying some liquid soap to the area. Bubbles indicate leakage (if there is still Freon in the system).
    la29freeman's Avatar
    la29freeman Posts: 4, Reputation: 1
    New Member
     
    #6

    Jun 17, 2009, 10:05 AM

    Feeon is good and no leaks. All vents are flowing freely with none of them blocked off. Air filter is clean and we checked the coil to make sure it was not dirty.. it was clean also.. still freezing up in basement and LOTS of condensation coming off the line that flows from the outside unit to the inside.. HELP!!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jun 17, 2009, 11:13 AM
    I would bet that the unit is not charged properly. I would call the company back that replaced the compressor since they would have charged the system after they installed the compressor. Since you have already checked the underside of the coil and said it was clean,and you said the filter was changed and the air was flowing then it would almost have to be charged incorrectly. This needs to be checked by a professional since they have the required EPA permit required to remove or dispense refrigerant. They also have the guages and know how to read them to judge the superheat or subcooling depending upon what type metering device you have installed for your indoor coil.

    What I do wonder about is the fact that if the coil is frozen over on the inside usually no air movement will be felt since the coil freezing blocks all the air flow. Could be you could shed some light on this subject since I have never seen a system move air at all when the coil is frozen up UNLESS the coil is installed improperly allowing too much air to bypass the coil itself. If that is the problem then that would also cause the coil to freeze up.

    Dirty coil as seen from the under side and dirty blower motor and wheel assembly.
    Attached Images
      

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ac freezing [ 2 Answers ]

My inside unit freezes up after running for about an hour. For the past three years, at the beginning of summer we have to have it recharged. Last year it was low three pounds. I have had three different companies come out and inspect and they say they cannot find any leaks. Where is the coolant...

Refrigerator freezing things and freezer barely freezing items [ 1 Answers ]

We have a Maytag MFF2557HEW, French doors on top and Freezer on bottom. We have freezer set at 7 and refrigerator set at 1. We cannot use veggie drawers because it freezes everything in them. We have to put all veggies and fruits on the shelves. Ice cream remains soft in the freezer, but meats...

Freezing up [ 2 Answers ]

Why is my coils in the attic freezing up ithought it only freeze up outside.what can I do to fix it

Freezing Ref [ 2 Answers ]

I have a refrigerator that occasionally will freeze product on Ref side. I happens about once each month. What could the problem be and what can I chaeck or do? Thanks

Freezing [ 1 Answers ]

Hi, My computer freezes when I am trying to watch Internet TV or stream video. Does anybody knows what is the problem? Tx


View more questions Search