    220Volts vs 240Volts and amperage draw
    Hello.
    I have had a tankless water heater installed in my house now for 2 years. The unit keeps tripping the circuit breaker whenever the hot water is turned on for an extended time (15 minutes).

    The unit is rated for 220 volts or 240 volts, however, the sticker on the unit only contains the wattage and amperage for 220 volts, which are 54a and 11.8kw.

    My electrician would only install a breaker capable of handling 54 amps (70 amp breaker and AWG6 wire). He says the reason it continues to trip is due to the fact Canada uses 240 volts, which will make the water heater draw more current than the sticker on it indicates. He wouldn't go higher because he needed to cover his butt.

    Can I increase my wire size to AWG4 and breaker to 80 amps without burning my house down?

    Thanks/Dan
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 22, 2009, 04:20 PM
    There is no way that should be tripping a breaker at 240v.
    Everything residential, with few exceptions, is 240v now in North America. Canada and the US have the same systems.

    Your tankless is rated at 54A @ 220v. This is 4.07 ohms.
    The same 4.07 ohms at 240v is ~59 amps and 14,138 watts.

    True, it should be on an 80a circuit, but 59a should not trip a 70a breaker, ever.

    Unless the #6 is in conduit the whole way it is not even rated for 70a, at least as far as the NEC is concerned, but this should not affect the breaker tripping either. Unless of course the circuit run is extremely far like 100'+.

    Did anyone ever come out and check the running amperage?
    DeltaPapa's Avatar
    DeltaPapa Posts: 2, Reputation: 1
    New Member
     
    #3

    May 22, 2009, 04:26 PM
    Yes the running current was checked. If I remember correctly, it was 61 or 63 amps. As for the run, it's about 25' of #6 wire that is in a flexible conduit similar to BX cable.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service amperage [ 4 Answers ]

I am stumped on this I need to now the total net load and the total load service for a 1800 square foot home with 11 kW range and a 6 kW 240 V dryer I have looked at the back of the NEC and I need to check my answers thank for any help?:mad:

Amperage capacity [ 3 Answers ]

Upgraded our circuit breaker to 20 amps for each slot. Is it possible/ safe to use one slot (20 amps capacity) for light bulbs and a garage door motor? The breakdown are as follows: Kitchen > 4 fluorescent bulbs 40 watts ea. Dining > 1 30 watts curcular bulb with ceiling...

Breaker amperage [ 1 Answers ]

What amp breakers are typiclly used in residential for dryer , washer, dishwasher, glass cooktop, separate oven, 4 ton package unit, bath gfi, etc?

Amperage for 20 amp breaker [ 4 Answers ]

I have 30 women with sewing machines in the same room. They all are using basically the same amps... 12 amps. How many breakers do I need and of what ratings?

Circuit amperage [ 2 Answers ]

If I have a 15 amp circuit does that mean I can only run one 15 amp rate device on that circuit? Or can I run any number of 15 amp or even higher amp devices, with wattage being the criterion for not overloading the circuit?


View more questions Search