    Lennox 2 speed inop.
    I have a lennox 2 speed condensing unit that is 25 yrs old and had very little problems with it. I cut the unit on last week and nothing. I took the panel off the outside unit to ck to see if I had voltage at the transformer and voltage coming from the house all good. I pushed the contactor in for the condensing fan and it worked. I did the same for the low speed and high speed contactor for the compressor and it also worked. The thermostat in the house allows the fan to come on and the high and low speed light on the thermostat to come on depending on temp. demand. I can hear the relays come on the unit outside. I have already replaced both potental relays last year due to the unit not shuting off. I had a repair man tell me that I needed to replace the unit last year. I figured this one out by myself. I also replace the time delay last year. What is the sequence of operation for this unit. To bypass the thermostat do I jump the same red and yellow wires? There is also two protection devices. I really would like to fix it can't afford a new one right now.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jun 9, 2009, 07:41 PM
    Sounds like a low voltage problem, with the tstat calling for a/c carefully check the tstat wire that connects to the contactor for 24 volts. If none start tracing the tstat wire looking for breaks or chewed wire an animal might have gotten to
    But yes to bypass tstat u can disconnect red and yellow wires at the tstat and tie them together ,should make a/c come on

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lennox Furnace fan only runs on slow speed in heating mode [ 4 Answers ]

I hope someone out there can help me under the control logic and components on my 1994 Lennox G20RE gas furnace. My fan runs at normal speed when it runs alone. When the furnace is in the "heat" mode, the fan only runs at minimum speed. It then overheats and begins to smell like it's burning up....

Telephone inop [ 1 Answers ]

I have ATT DSL which uses the same line as the telephone. This morning the phones worked but tonight I do not have a single phone in the house that works. No dial tone but yet the DSL works fine. I have gone through house unpluging the filters one at a time but still don't have a dial tone. No...

2000 Silverado - 4x4 inop [ 2 Answers ]

2000 Silverado 1500 keeps showing Service 4WD light... we replaced the switch in the dash, the encoder motor on the transfer case, the actuator, the module behind the switch, checked the ground wires, traced all of the wiring... nothing's worked! :mad: Occasionally, when you switch the key on...


View more questions Search