    Compressor is bad?
    House not cooling and HVAC man comes out this AM and looks at unit then goes into attic. Invoice says compressor not pumping and metering device is fixed. Home warranty company sends out 2nd man for verification and he confirms first diagnosis except he explains everything. He shows me on the guages that both sides are rising instead of one dropping and one rising. It seems to the compressor is pumping if there is a pressure change. Right?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    May 2, 2009, 07:23 AM

    Hard to tell, sounds more like just a restriction in you line or metering device. But a compressor can run, but not pump as much as it is supposed to. This will give you high readings.
    ge_krueger's Avatar
    ge_krueger Posts: 2, Reputation: 1
    New Member
     
    #3

    May 2, 2009, 09:18 AM

    Tech said suction valves are bad...
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    May 2, 2009, 09:20 AM

    Suction valve I assume means suction line king valve. That can be replaced.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #5

    May 2, 2009, 09:21 AM

    Or does he mean compressor valves?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #6

    May 2, 2009, 09:37 PM
    Sounds like the first tech got it right. Your compressor can run and not pump refrigerant(bad valves) and for his notes it was a piston type metering and not a expansion valve.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air Compressor doesn't run [ 10 Answers ]

I have 4 year old husky air compressor that quit working. I thought the motor burned up so took it in to have fixed, hooked up power and worked fine. The guy says it's my power source. It's a 240v motor 15 amp wired directly to my panel with separate breakers. I have 119 volts at each wire through...

Air compressor [ 1 Answers ]

1a/ a rotary air compressor increases the absolute pressure of the air from 100 kNm-2 to 230 kNmm-2 and the specific volume of the air is reduced from 0.7m3 kg-1 to 0.46 m3 kg-1. If the internal energy of the air is increased by 40 kj kg-1 find the change in enthalpy of 8 kg of air. b/ If at...

Compressor off/ fan trying to run [ 2 Answers ]

The fan on my Rudd unit keeps clicking like trying to start. I replaced the contactor. It didn't correct the problem. I called a service tech. He checked it out and said everything was fine. He replaced a flag connector. I had wired the new (double contactor) in for single pole. He moved the line...

Cannot get Air-compressor or fan to come on [ 1 Answers ]

I am having trouble getting the air-conditioner to come on. I have a five wire system very old Williamson thermostat for a Williamson natural gas furnace with an out side air-conditioner unit. The coils are above the furnace connected to it in the basement. I have replaced the old thermostat...

Compressor [ 1 Answers ]

If air compressor is froze or locked up will it always throw a breaker or a relay


View more questions Search